cu advice gladly needed ...... | Page 2 | on ElectriciansForums
Discuss cu advice gladly needed ...... in the Australia area at ElectriciansForums.net
E
ez2own
Right gentlemen need to ask your advice , thanks in advance ..
Going to change cu to a 15 way with split rcd to bring up to 17th/part p , original board is 14 way with rcd protected on main switch only .
My only concern is small 4 way cu in garage ( if i rcd protect will possibly trip main board in house if anything went pear shaped , would i be best to leave small cu in garage with rcd protection , but place into house cu with rcd not connected to garage supply.
only supply garage has external is 2 lights on a motion sensor .or would no rcd in garage be a non comply ????
Thanks again ...
Seems you are the only one that knows, that your not relying on a ground to trip an RCD. having two separate ground points will make little to no difference at all ...lol!! But your house connection point on your drawing is in the wrong place. lol!!
Glennspark,
The ONLY way to ensure discrimination between similar rated RCDs, is by a time delay.
Iv'e known 30mA and 500mA having no discrimination between them...
Ok. and thank you eng....I will be sure to keep this in mind....
Hang on I’m shipping water here!
E54
As I read the OP the house would have a RCD feeding the main CU, off which a SWA would feed a second RCD protected CU. Sorry if I misread anything.
Glen
With the set up as in my drawing any fault in either the garage or house would trip the house first.
This is in reply to Glen.
One thing you have to take in to account is there will be a slight leakage from the house circuits added to any leakage from the garage.
So say you have 10mA leakage in the house (PC’s, fridges Etc.) it’s effective range is now 20mA, where as the garage remains at 30mA.
The question remains the same, which trips first?
I'll put my neck on the block and say you can never truly say. Either or. Their individual characteristics are not guaranteed to remain steadfast as already mentioned many variables can affect, like ambient temperature (are they sited in different environments for example) , or as another possible when did they both last trip, I was taught that they do get a little sticky sometimes if not been tripped (either from a fault or by test button ) for a while and they pick up a little "lubrication" shall we call it when tripped.
Fix bayonet!
OP the other killer with the existing setup is when the garage is some distance from the house ... just done a similar thing at a property where the garage is 100M from the house. And yes, one RCD was covering the entire 2.5 acre site with 5 buildings dotted around ...... Arrrghhh
E54
Glen
Just looks to me as the house connection, is shown halfway along the Sub-main to the garage....
I would say that there is more than an even chance that both RCDs will trip, both will in all probability see a tripping fault current. As i say there is only one sure way to ensure discrimination and that's via a time delay in the upstream device.
you are correct Eng, it should be taken below the diagram for the house rcd now above it, sorry tony, i looked but couldn't find a suitable cartoon ;)
art_bailing_water_from_boat_hg_clr.gif Tony? ......................
But my thinking was that if the garage feed was taken off an MCB and not an RCD then the garage board is given RCD protection for final circuits in the garage then surely this setup will not affect RCD protected circuits within the house....i didn`t mention inline RCDs....
that's what i'd do, as the house cu is being replaced anyway. Split board with rcbo/mcb on one neutral bar with the rcd covering the other, take the garage feed from an mcb. Alternatively as Nick suggested a high integrity board with 3 neutral bars.
Reply to cu advice gladly needed ...... in the Australia area at ElectriciansForums.net
You cant just "avoid" the use of RCD's for nuisance tripping... it will depend on how the cable is routed. (ie buried less than 50mm) What has...
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...