Eng on a PME system the main bond is sized according to the supply neutral. The main earth then has to be sized according to the bonding conductor (542.3.1).

PME; size the bond then the earth.
TN/TT; size the earth then the bond.

Out of interest, why don't you 'totally agree' with my last statement?

Haven't done too much in the way of PME for a good few years now, so i'll have to have a gander at the Reg's on Monday when i get back to the office to see what the so-called official version is. I can't remember sizing the main earth conductor from the bonding conductor on a PME install though.

Personally, i'd stick with the 50% rule, even with a PME installation for the main earthing conductor, especially in these day's of plastic service pipes becoming more and more prevalent in the domestic sector. To be honest, can't think of any domestic PME heads that i've seen, converted or otherwise, that had just a 10mm main earth coming off the heads N/E connection to the MET, (...may be some very early heads had a 10mm connections). It's always been 16mm, (or larger when when the head has been a substantially bigger 3 phase supply on a commercial or small industrial installation).


I'll go along with the 10mm earthing conductor in this instance though, for a known 60A supply!! I certainly wouldn't be leaving the PME connection behind in favour of a typical UK TT system that's for sure!! lol!!
 

Reply to Cu Change Main Earth HELP! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top