CU Replacement on old TT system

V

Vessy

Hi all, first post for me, been a brouser of this site and all it's great info for years.

Looking to replace an old (fuse wire) CU in a 70's house, overhead cables and TT setup. There is a Chilton ELCB installed in the meter tails to the existing CU, the unit is a Type-E 60A 500ma ELCB (Black Unit), no earth connection just the two meter tails in and two out. Will be installing a split load unit comprising of 100A main switch feeding 1 83A 30ma RCB feed and 1 60A 30ma RCB feed, plus relevent MCB's.

Should I leave the old ELCB in place or ditch this as I will have all circuits covered by 30ma RCB's?

The unit works, just doesn't offer me anything above the protection in the CU. Not planning to have any MCB's before the RCB's.

Thanks.
 
no need for the 100mA RCD. that used to be fitted on TT systems, but is now redundant when fitting 30mA RCD to all circuits.
 
Purely for information, the obsolete Voltage Operated Earth Leakage Circuit Breakers mostly (but not always) have a yellow test button and (always) have a terminal labelled 'F' or 'Frame'.
 

Attachments

  • VOELCB[1].jpg
    VOELCB[1].jpg
    33.8 KB · Views: 50

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Back
Top