Just carried out an EICR on a flat that was wired in the 70s - with singles run in earthed conduit to each point and the trunking providing the earth at each socket/light point.
Ground floor flat, so needs RCD protection on sockets at least and seems due a CU change, but I have no experience with metal trunking so would appreciate the benefit of those with more experience...
Upper board can go as there is now a combi and central heating - no off peak circuits being used....
The lower board has approx 8 conduit lengths coming up, and 2 from above...All seem to be correctly glanded to the board - and the ZS readings at all sockets/fittings seem to be fine...
Obviously the chances are nil of finding a board to exactly match what's there - but I'd rather minimise the work - not to mention not having the skill or experience on metal conduit work (and this not being an empty flat where I could learn on the job).
What's the best way to ensure continuity with a new board?
1 option I can see is to leave the existing board in place purely as a 'junction box' for the earths and singles.... and fit a new one above it - leaving only the two upper conduits to deal with.
Another would be to replace the lower board with plastic trunking - terminating all the lower conduit with their existing bushes , but then I'd need to find a way to ensure continuity across the trunking - really don't want to have to cut metal trunking to do the job as it maybe 'should' be done.
If they are cut back, is there an approved clamp or similar to earth them, without needing to thread them for the correct glanding? I've found what is called a bonding nipple that looks like it would still allow space for the singles to exit.
Follow up question - all the sockets I checked have adequate Zs, but are getting that through the socket screws to the earthed back box (with the trunking glanded into each box). There are no fly leads from the box to the earth terminal on sockets. Some of the boxes have a terminal, to make that easy but others do not - but could be screwed, and drilled with self tapping and ring terminals used to make fly leads....
That is apart from the one more recently added socket which had a plasterboard backbox and earth cut short ? (Currently out of use until I can fix it)
In terms of an EICR on an existing installation, would you consider it essential to add the fly leads, a recommend, or not necessary at all as long as the earthing is satisfactory?
Final Question - Easycert has the option to choose 'conduit' for the earthing sizing on the test list. Is there any check that needs to be done to ensure equivalent sizing, or is pretty much all conduit greater than the equivalent T&E sizing?
Ground floor flat, so needs RCD protection on sockets at least and seems due a CU change, but I have no experience with metal trunking so would appreciate the benefit of those with more experience...
Upper board can go as there is now a combi and central heating - no off peak circuits being used....
The lower board has approx 8 conduit lengths coming up, and 2 from above...All seem to be correctly glanded to the board - and the ZS readings at all sockets/fittings seem to be fine...
Obviously the chances are nil of finding a board to exactly match what's there - but I'd rather minimise the work - not to mention not having the skill or experience on metal conduit work (and this not being an empty flat where I could learn on the job).
What's the best way to ensure continuity with a new board?
1 option I can see is to leave the existing board in place purely as a 'junction box' for the earths and singles.... and fit a new one above it - leaving only the two upper conduits to deal with.
Another would be to replace the lower board with plastic trunking - terminating all the lower conduit with their existing bushes , but then I'd need to find a way to ensure continuity across the trunking - really don't want to have to cut metal trunking to do the job as it maybe 'should' be done.
If they are cut back, is there an approved clamp or similar to earth them, without needing to thread them for the correct glanding? I've found what is called a bonding nipple that looks like it would still allow space for the singles to exit.
Follow up question - all the sockets I checked have adequate Zs, but are getting that through the socket screws to the earthed back box (with the trunking glanded into each box). There are no fly leads from the box to the earth terminal on sockets. Some of the boxes have a terminal, to make that easy but others do not - but could be screwed, and drilled with self tapping and ring terminals used to make fly leads....
That is apart from the one more recently added socket which had a plasterboard backbox and earth cut short ? (Currently out of use until I can fix it)
In terms of an EICR on an existing installation, would you consider it essential to add the fly leads, a recommend, or not necessary at all as long as the earthing is satisfactory?
Final Question - Easycert has the option to choose 'conduit' for the earthing sizing on the test list. Is there any check that needs to be done to ensure equivalent sizing, or is pretty much all conduit greater than the equivalent T&E sizing?