Hi all. Not a working butnvq 3 after 3 yrs at college . Looked at wife's friends cu for her. Was tripping out at random. Checked RCA times and current all ok. Cu box looked rough with large hole in the top and two bare wires poking out. Checked insulation resist of main ring got 340ohms but didn't have time to check further. Also noted that all but one phase and neutral were all loose, and the cooker and old shower cables had melted together. Removed old shower cable and made good connections and burnt wire. Main switch seemed to be rated at 63amps and as client asked for a new shower to be installed I thought that cu would need upgrading even tho it's mcb and rcd.
advised her to ask someone more knowledgable than me.
professional came in fixed tripping( bad socket upstairs) and said box ok for shower its not very old. Wiring In place is 10mm and said he would go away and come back with a quote.
Question is this. Is the 63amp rating on main switch ok for a box feeding a ring main,immersion heater, electric oven and hob, and 9kw shower and lights etc or am I misunderstanding something.

I realise I have to tell local building control of work and present them with my works done and test results. For a certificate

I'd be interested to hear what some of the more experienced chaps say to this as it does seem afair bit for a 63A switch.

If you use the OSG diversity then you've got 32A for the ring and 39A for the shower straight away so your up to 71A without any of the other circuits taken into account.

However if you use the guidelines from some DNO that does seem to get mentioned a fair bit, then you add up all the breakers and multiply by 0.4 View attachment DNO guidelines on Max demand - GOOD.pdf so perhaps (40+32+32+16+6+6) x 0.4 = 52.8A.
 
Eng54 will be along shortly to tell you to clamp it and then be surprised at how low the reading is! Daz
 
she's bloody gorgeous Daz
 

Reply to Cu upgrade or not ? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

  • Question
It’s quite common for an electrician to criticise another’s work as you will rarely get everything perfect.
2
Replies
20
Views
1K
N
  • Question
He hasn't provided any certificates, including previous work. He sends invoices when he needs paying.but no vat registration number etc on...
  • Nessab16
  • Ireland
  • 8
  • 535
Replies
8
Views
535
Nessab16
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top