current carrying capacity | on ElectriciansForums
Discuss current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net
belfast
can anyone help please,
I am testing a new installation for another contractor, lighting circuits are wired in 1.5mm pvc singles in 4inch metal trunking, protected by 16amp type c mcbs, is this overated considering correction factors applied? thanks
This might be a daft idea but if you are carrying out initial verification could you not consult the installation design paperwork? You do of course have this as you are verifying the installation against this as well as bs7671
there maywell be a bit of derating there! unless all 18 are rather lightly loaded!
Or unless there isn't a total of 288A supply capacity, in which case you can't run them all at full whack anyway. They might be C16s to avoid tripping on inrush, but only loaded to say 5A with a fixed load. In which case it might not be as bad as it looks...
Reply to current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net
You don't normally see It in the equation. What you would normally do is apply correction factors then select a cable/conductor for Iz from It...
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...