belfast
can anyone help please,
I am testing a new installation for another contractor, lighting circuits are wired in 1.5mm pvc singles in 4inch metal trunking, protected by 16amp type c mcbs, is this overated considering correction factors applied? thanks
Or unless there isn't a total of 288A supply capacity, in which case you can't run them all at full whack anyway. They might be C16s to avoid tripping on inrush, but only loaded to say 5A with a fixed load. In which case it might not be as bad as it looks...
7671 allows for this with the paragraph below the grouping table. Although they do have to be very lightly loaded to avoid being included in the calculation, hence my comment.
What's with all the bloody eh's eeeh's arghhhhhs and ohhhh's then
Can ya lot nay speak proper english like eye yused to did
There are two separate points here interestingly, and I was focusing on the other one to yours. As you say, if a circuit has a fixed load much lower than its ungrouped capacity, it can be discounted because it will never dissipate much heat. OTOH if heavy diversity has been applied, even where the circuits can each be heavily loaded, it might not be possible to load more than a few at a time. E.g. twelve 10A circuits each with 10A load, but all running on one 60A supply. It's only possible to load half of the circuits fully, and this will always be a worse case for cable heating than the same 60A divided between more of the circuits*, so only six contribute to the grouping.
*Seems obvious to me and can be proven in three lines of math, but I had the devil's own job convincing some sparks of this once.
It's a situation that often occurs in stage lighting. E.g. 96 circuits all protected by K10 MCBs, but running on a total of 3x60A. Only 18 can be fully loaded at once, but in practice it's more likely to be 41 circuits loaded with 4.4A, which requires less derating even though they are above 0.3CgIt.
Not that this applies to normal commercial or industrial lighting though.
And then Mr self proclaimed LX expert comes along and types 1 thru 96 @ full enter ;)
And then the lights come on, and then they go off again in a rather terminal fashion thanks to Mr MCCB esquire.
Reply to current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net
You don't normally see It in the equation. What you would normally do is apply correction factors then select a cable/conductor for Iz from It...
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...