I've just seen an install fitted 2 years ago and I'm interested in how this is G83 compliant! information regarding design etc is being forwarded to me later, but what they've done seems like madness/sheer incompetence to me
I'm going to call the company on clients behalf and hope they sort it as its a shambles this will be the 5th return visit from this firm
There are 2x Aurora 3000 inverters and one 3600, (not sure if Tl's or not i'll be checking later) each has its own Rcd and Mcb fed via 4 wy CU next to the inverters and the single phase supply is daisy chaining across each CU Rcd top terminals
System has worked without issues but recently the Rcd covering the 3600 is tripping out so customer called me in to have a look,
Other than what I've already mentioned above the cable feeding these has no isolation or relevant ocpd and is dogged into the incoming side of the DB main isolator , they've fitted 2 AC isolators next to each inverter and the supply goes through the Rcd (also daisy chained to the next Cu) and Mcb then through the meter and then to the first Ac Isolator and then the 2nd????
Also they have Dc cables in the same 50x50 trunking which I know is debatable re the insulation rating but something I'd not do.
9 feet away is the mains incomer with a 3 phase supply! it is such an easy job to have done better I'm staggered!
I'm going to call the company on clients behalf and hope they sort it as its a shambles this will be the 5th return visit from this firm
There are 2x Aurora 3000 inverters and one 3600, (not sure if Tl's or not i'll be checking later) each has its own Rcd and Mcb fed via 4 wy CU next to the inverters and the single phase supply is daisy chaining across each CU Rcd top terminals
System has worked without issues but recently the Rcd covering the 3600 is tripping out so customer called me in to have a look,
Other than what I've already mentioned above the cable feeding these has no isolation or relevant ocpd and is dogged into the incoming side of the DB main isolator , they've fitted 2 AC isolators next to each inverter and the supply goes through the Rcd (also daisy chained to the next Cu) and Mcb then through the meter and then to the first Ac Isolator and then the 2nd????
Also they have Dc cables in the same 50x50 trunking which I know is debatable re the insulation rating but something I'd not do.
9 feet away is the mains incomer with a 3 phase supply! it is such an easy job to have done better I'm staggered!