I have today come accross my first polarity problem.
while checking a socket i found it was showing reverse polarity with L and N.
After checkig behind the socket and all other sockets on the same ring all were correctly wired.
I checked the polarity of L and N at the consumer unit and although also wired correctly this also showed reverse polarity. The job was in one of three flats so were sub mains from the basement where the meters are. In the basement each flat has its own main fused switch from its own meter. On checking this main fuse switch it also showed reverse polarity but was correctly wired.
When i say correctly wired in all cases i mean all Neutrals were black sheathed and all line conductors red sheathed.
However, the tails from the meter to the main fused switch pass via a 100A connector block. In this block both black neutral conductors correctly go into th front connector and both line red conductors go into the rear connector block.
I am assuming the problem is then at the exit from the meter where Line and Neutral must incorrectly wired.
The only identification at the meter is the colour of the sheath so I can do no other check.

Leaving the meter I believe the Neutrals are always side by side in the middle and the two lines are on either side ( L-N-N-L ) but in this case they are ( L-N-L-N).
Is this just a straight case of contacting the supplier to rectify a dangerous situation asap or am I missing something?
 
If you have tested at the CU and the supply coming into it is reversed you need to isolate the main switch and contact the DNO immediately and have it rectified..

Its your instuments that you have to take note of not the colour of the conductors.

I take it that you are testing with an approved voltage indicator etc.
 
Near 24hrs later and have you done anything?
If anything goes wrong your necks on the line as well as the DNO's. If you know of a dangerous situation and do nothing your equally as liable as the fool who wired it in the first place.
 
pull the cut out fuse take the meter cover off on the back of the cover will be a wiring diagram and most likely it will be l n n l job done
Why would you WANT to do this??, Make it safe (isolate lock off main switch, then call DNO) they will class this as a high priority and will be out VERY quickly, in my experience they attend dangerous situations often within an hour. Personally I Never cut meter seals as thier is never a need too, leave that for the DNO
 
there are sparks or people who have near misses every day ,its just a fuse
i replace fuses every day sometimes under load, most times off load most fuses blow due to a fault condition there is not one here just a polarity reversal
iv`e been involved in cu changes for councils and we always pulled our own fuses iv`e also had my apprentice wire from the meter to cu exactly the same way as this resulting in the smoke detector blowing up but you learn to get on with it
you cant isolate a customers premises then wait for dno to come out
your a spark get on with it
 
there are sparks or people who have near misses every day ,its just a fuse
i replace fuses every day sometimes under load, most times off load most fuses blow due to a fault condition there is not one here just a polarity reversal
iv`e been involved in cu changes for councils and we always pulled our own fuses iv`e also had my apprentice wire from the meter to cu exactly the same way as this resulting in the smoke detector blowing up but you learn to get on with it
you cant isolate a customers premises then wait for dno to come out
your a spark get on with it

Being a spark is one thing, breaking the law and working outside the scope of HASAWA is another. How do you fancy the fraud squad knocking on your door because meter seals have been cut? It can happen, and it's up to you to prove. If I was passing your house and decided a tree in your garden looked like it would fall down, would you rather I took it upon myself and cut it down, or would you rather I contact you (the owner) with my concerns?
 
there`s not a spark on here who hasn`t cut the seals off and whos to say you cut it off

I BEG YOUR PARDON Sorry I have cut seals on main fuses but with AUTHORITY AND TRAINING I Never advise this option specialy NOT on the forum as
1 you dont know how competant the person your advising is
2 you have no knowlage about the cable head type
3 you cant see the condition of head bakalite broken ect ect ect FFS I WISH GUYS WOULD STOP saying PULL IT willy nilly
 
Last edited by a moderator:

Reply to Dangerous reverse polarity on meter tails in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
889

Similar threads

yeah so it looks like an old off peak heating circuit to what would have been storage heaters my preference is to remove them completely from the...
Replies
2
Views
277
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top