yeah i just noticedYes they are on this thread somewhere
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Dangerous upgrade to crabtree rcbo's in the The Welcome Forum area at ElectriciansForums.net
yeah i just noticedYes they are on this thread somewhere
Yes page 3 I think.. Not really into the electronics side so all too much for me but don't like it when people go from a blue wire to a white wire and back to blue again.. Makes u wonder if its all wired correctly as it should be as like I said the old style rcbo didn't have this problem.. Can probably take some more pictures if anyone wanted..yeah i just noticed
The pics are on page 3 if u haven't seen them already..That broke my mind - can you post a pic please?
page 3 of The Sun? yummy pics, they were.The pics are on page 3 if u haven't seen them already..
Thanks freelec for the update on this, I had nearly forgotten about this but shouldn't have as the amount of worry over working live this thread caused kept me replying for a while .lol??I realize this post is over a year old but I have some info that may clear this up. Don't know if anyone will see this now but I thought I'd post it anyway.
I recently had the same issue getting a light shock off the neutral flylead.
After looking up the specs of this RCBO I found the reason.
They claim 2 things about it. 1/ That is is double pole. 2/ You can IR test the circuit with the breaker off.
This can only mean that the electronics are on the supply side and not the load side. Hence, when connected to the busbar the flylead becomes live.
The leaflet that comes with it says to isolate the busbar but as has been pointed out, this is the real world and EAWR does allow live working. Irrespective of that they should have labeled the RCBO clearly that the flylead becomes live on connection and the electronics are on the supply side. A circuit diagram on the side is not enough.
The claim is that you don't have to disconnect conductors to do an IR test. I would rather do that than have this situation. One poster said that you can connect the flylead first which is exactly what I did on the others that I instaledl. However, you shouldn't have to do it that way as how do you dress it in round the other wires without a great deal of hassle.
This had been dangerously designed for one simple reason. Any experienced spark knowing how RCBOs work would not expect the electronics to be on the supply side.
Another thing. What if there was a problem with the electronics itself. You wouldn't be able to turn it off without isolating the whole board and removing it.
Very poorly thought out, and for what? Being able to IR test without removing conductors.
Next they'll be making them with four terminals so you can ring continuity test without removing conductors.
Reply to Dangerous upgrade to crabtree rcbo's in the The Welcome Forum area at ElectriciansForums.net