You wouldn't want to put them in separate pieces of metal trunking or you will be giving yourself a couple of nice size electro magnets!!
Surely this wouldn't be an issue with DC?
I think with DC would produce electromagnetic effect of some sort, with AC you would get eddy currents, correct me if i'm wrong.
Providing mechanical protection sufficient to prevent penetration be nails or screws is just on of the acceptable methods of providing additional protection.you can run DC in SWA.
The regs require cable buried at less than 50mm to be mechanically protected against nails screws and the like. It also says SWA may not satisfy this requirement. Also how will you keep within your zones?
I am very reluctant (as in, never have) to run DC anywhere inside a house except clipped onto the rafters in a loft and clearly labelled.
Is the client also going to be running his drainpipes inside the house, because in all honesty a bit of conduit looks no different!!
I agree the nail will win. but provided the armour is earthed there should not be a drama
spinlondon said:As such SWA doesn't have to satisfy that requirement, as it satisfies another, insofar as the armour is an earthed metallic sheath.
but they'd also detect a short circuit on the DC side anyway.Most inverters will also detect if one of the dc cables is taken to earth and will then cut out. So the user can notice something is wrong.
But usually bonding is between conductors that all have potential to earth. In this situation there is no potential to earth from the DC side of the circuit, so you could hold the bear live end of the positive DC cable in one hand and touch the water pipes etc all day long with no problem.It should not really matter what potential it was at from a safety perspective if everything was at the same potential, which is the point of bonding.