4.1 Requirement as per DIN VDE 0100-712 (IEC60364-7-712:2002)
If intended as fault protection (see Section 2.2 "Automatic Disconnection via Residual-Current Device" (page 6)), DIN VDE 0100-712 requires a type B residual-current device for transformerless inverters.
This requirement also applies to inverters with HF transformers, since there is no galvanic isolation between the
AC current side and the DC voltage side.
One exception to this is if the manufacturer of the inverter can exclude the possibility of DC residual currents in the system. If necessary, type A residual-current devices can be used.
All SMA inverters with transformer, including SB 2000HF-30, SB 2500HF-30, SB 3000HF-30, and the
transformerless SMA inverters listed below are not capable of feeding-in DC residual currents due to their
design. They fulfill this requirement in accordance with DIN VDE 0100-712 (IEC60364-7-712:2002).
Sunny Boy:
SB 1600TL-10, SB 2100TL, SB 3000TL-20, SB 3000TL-21, SB 4000TL-20, SB 4000TL-21, SB 5000TL-20,
SB 5000TL-21
Sunny Mini Central:
SMC 6000TL, SMC 7000TL, SMC 8000TL, SMC 9000TL-10, SMC 9000TLRP-10, SMC 10000TL-10,
SMC 10000TLRP-10, SMC 11000TL-10, SMC 11000TLRP-10
Sunny Tripower:
STP 8000TL-10, STP 10000TL-10, STP 12000TL-10, STP 15000TL-10, STP 17000TL-10, STP 15000TLHE-10,
STP 20000TLHE-10
The possibilities of faults were examined without taking the integrated residual-current monitoring unit (RCMU)
into account. When examining these faults in terms of the currently valid installation standards, no danger in
combination with a type A upstream residual-current device can occur. Accordingly, faults that would otherwise
require the use of a type B residual-current device due to the inverter can be excluded.
The integrated all-pole sensitive residual-current monitoring unit (RCMU) results in additional safety. For
inverters with grounding conductor monitoring, this must be activated. These statements also apply to versions
of the listed devices with deviating power