A switch disconnector shall be provided on the dc side of the inverter.
* The switch must isolate all live conductors (typically double pole to isolate PV array positive and negative conductors)
* The switch must be rated for dc operation at the system voltage maxima as calculated in section 2.1.2.
* The switch must be rated for dc operation at the system current maxima as calculated in section 2.1.2.
* The switch must be labelled as ‘PV array d.c. isolator’, with the ON and OFF positions clearly marked. Switch enclosures must also be labelled with ‘Danger - contains live parts during daylight’. All labels must be clear, easily visible, constructed and affixed to last and remain legible for as long as the enclosure.
* The switch should be located adjacent to, or integrated into the inverter.