Sensible yes, good practice, yes, in a multi string environment almost essential for maintenance and testing. Mandatory ... No as SMA have said it is adequate![]()
Version 3 of the guide says ..
So to the the letter it meets the final clause.
The guide goes on to say:
We ALWAYS fit DC isolators, because on an industrial sized installation the thought of pulling the ESS to break 17+kW of DC is horrendous.. On a recent job we used 4 pole isolators to work on two strings, however we are unlikely to be doing that again because when you make one pair live to test the string you've now got the other pair live also. also some of our strings run close to 1000V Voc and you get a b*****y great spark if you try to seperate those after doing an Isc test without first opening the isolator!
We have 4KWp panels (15 x 265w, 2 strings, one of 6 panels, and the other 9 panels). 15m DC cable run. The inverter is in the garage next to Consumer Unit.
Would you still be concerned an a 4kwp domestic install?