Hey,

Hoping someone out there has got an idea where i can pick up five 100A 1000V DC Isolators. Seem to be running into brick walls with all my usual suppliers.

Thanks

Tony
 
Yeah it's for a 250kwp job in a fortnights time. Last piece of gear to pick up ready
 
11 strings in parallel, inverter requirements built the string boxes yesterday to accommodate, drop from the roof structure in 2 core swa 50mm but want to isolate outside of the central inverter for maintainer purposes
 
11? I was assuming 10 x 20 panel strings. Unless you're not talking standard 30V, 8amp (ish) panels, wouldn't 11 strings take you over the rating for even a 100A isolator, once you include the x 1.25 derating factor?

Mono- and multi-crystalline silicon modules - All d.c. components must be rated, as a minimum, at: Voltage: Voc (stc) x 1.15
Current: Isc (stc) x 1.25
from http://www.microgenerationcertification.org/images/PV Book ELECTRONIC.pdf

not that MCS actually applies as such to above 50kWp installs, but it'd still be best practice to allow for this if you haven't already?

eta - this is a question more than a statement btw as we've not done anything outside MCS territory so far, so I'd be interested to know if companies are applying different methods above that limit.
 
Last edited:
Splitter boxes are on roof with pv string fuses and isolator. Lookin to isolated the feeds once inside the building. Was hoping to find larger isolator a so a to avoiding running even more lines into the building than I already am but looks like I'm going to have to
 