Hi, I have always made sure my installs have no departures from bs7671 but I'm doing a ccu change next week and have done some preliminary testing and the heating circuit (boiler and heating controls) has low IR readings, had a look in all obvious places and cant find any problems, had trouble breaking the circuit up as its a bit messy, client has just decorated so he doesn't want any damage to the house, seeing as its all fixed equipment (I'm unsure on the cable routes but id guess its buried less than 50mm at some point) is it acceptable to leave this circuit unprotected and note it on the departures section? all the earthing/bonding is mustard. Any experience on this would be appreciated, thanks.
 
With the greatest respect, don't "try" to rectify the fault, but make it clear that it MUST be sorted before you proceed further. If your test was 7 meg and that was an end to it, then all well and good. A note that IR tests were low would have covered you. However, as it is taking the RCD straight out, then there is something very wrong somewhere.
How would you feel if there's a fire due to this fault, and you'd walked away saying "I had a look, but nothing I could do"?
 
It would only be a c3 if doing a periodic and it was done to old regulations, but u are effectively updating the installation to 17th edition regs by applying Rcd protection, and as u say u think cable is in wall less than 50mm so to 17th obviously needs Rcd protection. But I would explain to customer that it needs sorting before changing Fuseboard, as you have tested circuit and it fails test so further investigation is required.
i also applaud you for testing installation prior as many don't, and has also potentially got you more money out of the job rather than sorting later at your expense/time finding and fixing fault.

Thanks for the reply, BS7671 does not require circuits to be upgraded to current regulations to be connected to a replacement ccu, only for it to be ascertained that they are not an immediate danger (which I would read as no C1's or C2's), GN3 even says there is no obligation to inspect or test any part of the installation!

Also found this : www.niceic.com/Uploads/File1950.pdf Guidance on cu replacement, which also says the same. interesting reading.
 
disconnect at the FCU> if it's only single pole, then take the N out of the terminal. then test your circuit. if the fault is on the heating then you need the customer to get it sorted, either by you or a heating " engineer" (that's usually a plumber that can read and write).
 
With the greatest respect, don't "try" to rectify the fault, but make it clear that it MUST be sorted before you proceed further. If your test was 7 meg and that was an end to it, then all well and good. A note that IR tests were low would have covered you. However, as it is taking the RCD straight out, then there is something very wrong somewhere.
How would you feel if there's a fire due to this fault, and you'd walked away saying "I had a look, but nothing I could do"?

That's not what Im saying, its a bit more complicated then that, it may be that the client does not want any work done in which case I need a reason for the circuit to be on a rcd, which to be honest there isn't
 
odawire, if you get the same reading L-E as N-E, then its one or the other with a load still connected. do continuity L-N first, then 250V L-N this will give you a better idea.
 
If you've got an IR measurement of 7MOhms, then you're chasing up a tree. 230/700000 = something too small to bother with, certainly not enough to trip a 30mA RCD. So, test and test again. Have you considered something as mundane as a borrowed neutral somewhere?
 
That's not what Im saying, its a bit more complicated then that, it may be that the client does not want any work done in which case I need a reason for the circuit to be on a rcd, which to be honest there isn't

I don't get this, maybe I'm misunderstanding you. It's not a case of whether the circuit should or should not be on an RCD. The issue is the fact that the circuit should work fine if it is on an RCD, but it doesn't. The reason you are putting forward for not protecting it with an RCD is not a regs issue, it's because it won't work when it is fed from one. Daz
 
I don't get this, maybe I'm misunderstanding you. It's not a case of whether the circuit should or should not be on an RCD. The issue is the fact that the circuit should work fine if it is on an RCD, but it doesn't. The reason you are putting forward for not protecting it with an RCD is not a regs issue, it's because it won't work when it is fed from one. Daz

My original question was about departures being noted on an EIC, but its turned into me turning my back on a dangerous situation which I haven't.

- - - Updated - - -

Just a thought I would disconnect any zone valves or circulation pump I know from experience they can be a pain

Thanks, ill keep that in mind
 
Hi, should have explained, I have a rig I made up I use sometimes, its basically an rcd adaptor that I wire into and plug into a socket, when I did this it tripped, the IR reading was bouncing around I think it settled around 7Mohms across all points, I remember it was the exact same number. The reason Im asking is, I want to know if its acceptable to leave it off the RCD side if I have to, as I don't think I can leave them with no heating at this time of year, can I note it as a departure as the cable is probably less than 50mm deep

Maybe you should go back and retest the IR as I wouldn't expect the value you claim to trip an RCD if it really was across all 3 "points"
 

Reply to Departures from bs7671, certification. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
747
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
745

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top