Hi, I have always made sure my installs have no departures from bs7671 but I'm doing a ccu change next week and have done some preliminary testing and the heating circuit (boiler and heating controls) has low IR readings, had a look in all obvious places and cant find any problems, had trouble breaking the circuit up as its a bit messy, client has just decorated so he doesn't want any damage to the house, seeing as its all fixed equipment (I'm unsure on the cable routes but id guess its buried less than 50mm at some point) is it acceptable to leave this circuit unprotected and note it on the departures section? all the earthing/bonding is mustard. Any experience on this would be appreciated, thanks.
 
Is it not right to do an EIC for the CU change and an EICR for the testing and inspection afterwards? Also if IR test is 7MΩ, it shouldn't be tripping should it?

No, you don't do an EIC and an EICR. You test the circuits before reconnecting to the new CU, and note the readings on the certificate. If they are non-compliant they should not be reconnected.
That said, if you have been asked to carry out an EICR in addition, then there's nothing wrong with that, but it will be a lot more in-depth.
 
No, you don't do an EIC and an EICR. You test the circuits before reconnecting to the new CU, and note the readings on the certificate. If they are non-compliant they should not be reconnected.
That said, if you have been asked to carry out an EICR in addition, then there's nothing wrong with that, but it will be a lot more in-depth.

I do basically agree with what your saying, but the problem is that an EIC does not account for anything outside 17th edition, which just isn't realistic, there must be situations where the CCU is changed but NCS cabling is connected.
 
Could you tell me where BS7671 states only an EICR is needed for a CU change please.

Good grief, is this thread the reincarnation of 2391? :)

GN3 to the ready, chaps.
 
Could you tell me where BS7671 states only an EICR is needed for a CU change please.

Its more what it doesn't say, EIC is required for a new installation or changes to an existing installation. It depends how you want to view a CCU change, If your not changing any fixed wiring or maybe just adding RCDs in which case you may not even be changing the protective device. And there are a lot of different opinion's on this, but obviously not on this forum
 
Its more what it doesn't say, EIC is required for a new installation or changes to an existing installation. It depends how you want to view a CCU change, If your not changing any fixed wiring or maybe just adding RCDs in which case you may not even be changing the protective device. And there are a lot of different opinion's on this, but obviously not on this forum

Right, you've answered your own question there so that's sorted at last. What are you going to do about the RCD issue then? Daz
 
Its more what it doesn't say, EIC is required for a new installation or changes to an existing installation. It depends how you want to view a CCU change, If your not changing any fixed wiring or maybe just adding RCDs in which case you may not even be changing the protective device. And there are a lot of different opinion's on this, but obviously not on this forum

EIC required. Can't imagine how anyone could understand otherwise??
 
Its more what it doesn't say, EIC is required for a new installation or changes to an existing installation. It depends how you want to view a CCU change, If your not changing any fixed wiring or maybe just adding RCDs in which case you may not even be changing the protective device. And there are a lot of different opinion's on this, but obviously not on this forum

Apart from a full rewire, a change of CU is probably the most onerous change to an installation you can make, to suggest that what certification you decide to use is down to interpretation is, frankly, ridiculous.
I would bet my house that if you went on the IET forum and postulated the same belief's you have here, you would be shot down just as quickly.
However, if you feel strongly about it, may I suggest you use an EICR for your board change and then use that same installation as one of the ones that gets inspected for your annual scam assessment.
 
Last edited by a moderator:
Its more what it doesn't say, EIC is required for a new installation or changes to an existing installation. It depends how you want to view a CCU change, If your not changing any fixed wiring or maybe just adding RCDs in which case you may not even be changing the protective device. And there are a lot of different opinion's on this, but obviously not on this forum

As the others have said many times now, it's not open to interpretation at all. A CU change is definitely a change to an installation and not open to debate. You will also find it stated in many publications that it requires an EIC.
All the people you have spoken to over the years regarding this matter are simply wrong if they have told you that an EICR is acceptable. Have you personally changed a CU and not issued an EIC by any chance?

As you are changing the CU, you are obviously with a part P scheme. Give them a ring and see what answer you get. :)
 
Apart from a full rewire, a change of CU is probably the most onerous change to an installation you can make, to suggest that what certification you decide to use is down to interpretation is, frankly, ridiculous.
I would bet my house that if you went on the IET forum and postulated the same belief's you have here, would be shot down just as quickly.
However, if you feel strongly about it, may I suggest you use an EICR for your board change and then use that same installation as one of the ones that gets inspected for your annual scam assessment.

If you read the thread you can see I don't feel strongly about it, Its something I agree with you guys on lol, what im saying is many of people I have talked to over the years have stayed strong with the idea of PIR for a CU change most of them interestingly enough from the IET, and your gonna have to explain that last sentence to me please as I don't like the sound of it

- - - Updated - - -

As the others have said many times now, it's not open to interpretation at all. A CU change is definitely a change to an installation and not open to debate. You will also find it stated in many publications that it requires an EIC.
All the people you have spoken to over the years regarding this matter are simply wrong if they have told you that an EICR is acceptable. Have you personally changed a CU and not issued an EIC by any chance?

As you are changing the CU, you are obviously with a part P scheme. Give them a ring and see what answer you get. :)

Yes I agree
 
and your gonna have to explain that last sentence to me please as I don't like the sound of it

On this forum, members generally refer to the different part p schemes as 'scams', in reference to the fact they do bugger all for your money and are simply contributing to an overall malaise in the electrical industry.

What I was saying in my last sentence was that if you feel that an EICR is acceptable paperwork for a CU change then use that same piece of work as one of the one's that you have your annual assessment done on. The implication being that you will get a -------ing from your scheme (scam :smilewinkgrin:) assessor.

Cheers
 
On this forum, members generally refer to the different part p schemes as 'scams', in reference to the fact they do bugger all for your money and are simply contributing to an overall malaise in the electrical industry.

What I was saying in my last sentence was that if you feel that an EICR is acceptable paperwork for a CU change then use that same piece of work as one of the one's that you have your annual assessment done on. The implication being that you will get a -------ing from your scheme (scam :smilewinkgrin:) assessor.

Cheers

Ok sorry, thought you were being out of order
 
Ok sorry, thought you were being out of order

No problem, and no apologies necessary.

Nothing on here really get's personal, apart from a few idiots who don't last long anyway, but you will find lots of peeps with forthright views who will defend them vigorously. Obviously sometimes 'vigorously' can get a little OTT.

Cheers
 

Reply to Departures from bs7671, certification. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
747
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
745

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top