Hi guys, after getting valuable info from previous thread and study my notes. After flicking through the BS book, and OSG i think i finally have my design iformation, for my assessment using my grandads shed/workshop as a rewire
If you guys could check it for me, i would be very grateful. And if your ever in the Biggin hill area, I buy you a beer for your time...haha
Right here goes:-
Circuits
Lights:- 2x 36w Florescents = 72watts
x factor for control gear lights 1.8
= 130watts (0.57amps)
Diversitiy of 66% = 0.38 amps. (will use a 6 amp MCB for this circuit)
Planer supply:- (Not to be installed but adding in calculations if added for the future)
This isn't working at the moment waiting for a new part for it. But its a 10amp
machine, but has a 23amp start up.
Diversity 100% = 32amps
Ring:- Consists of 4 sockets, with be running general electric tools, but in winter times may have
heaters to keep the old boy warm while he does his hobby stuff.
Diversity 40% = 12.8amps
Total Demand (max demand) = 45 amps (So will have a 63a RCD Main Switch 30mA)
-----------------------------------------------------------------------------------------------------------------------
It will have 2 conduit runs in PVC in stranded cable (Method B),
1 for Lighting 8 meters
1 for Ring 20 meters
Lighting = 1.5mm (L&N) 1.0mm (Earth)
Ring = 2.5mm (L&N) 1.5mm (Earth)
Lights:- Table 4D1A
CCC = 1.5mm Method B 17.5amp
VD = 29x0.38x8/1000 = 0.08v (0.03%)
Ring:- Table 4D1A
CCC = 2.5mm Method B 24a (i see this as ok as its 20 amp per leg)
VD = 18x26x20/1000/4 = 2.34 (1%)
---------------------------------------------------------------------------------------------------
Submains
25 metre run from under stairs in house, buried under lawn to shed, to cope with a Max deman of 45amps.
Be Thermoplastic 70degree armoured 16mm 3 core cable
Using table 4D4A and B
Say im using a 50amp isolation switch (over 3 metre rule) to cope with Max demand of 45 amp
CCC = 78A
Factors = Ca 1.00
Cg 1.00
Ci 1.00
Cc 0.90 (factor for burial of cable out of OSG)
= 78a x 0.90 = 70 amp (so good enough for 45 max demand)
VD = 2.4x50x25/1000 = 3volts (1.3%)
Plus adding the submain VD of 1.3 and my final circuit for my lighting 0.03%. All in all im well within the 3% Limit.
IS THIS RIGHT. OF HAVE I MESSED UP....
Sorry about the long read...
Thanks again guys
If you guys could check it for me, i would be very grateful. And if your ever in the Biggin hill area, I buy you a beer for your time...haha
Right here goes:-
Circuits
Lights:- 2x 36w Florescents = 72watts
x factor for control gear lights 1.8
= 130watts (0.57amps)
Diversitiy of 66% = 0.38 amps. (will use a 6 amp MCB for this circuit)
Planer supply:- (Not to be installed but adding in calculations if added for the future)
This isn't working at the moment waiting for a new part for it. But its a 10amp
machine, but has a 23amp start up.
Diversity 100% = 32amps
Ring:- Consists of 4 sockets, with be running general electric tools, but in winter times may have
heaters to keep the old boy warm while he does his hobby stuff.
Diversity 40% = 12.8amps
Total Demand (max demand) = 45 amps (So will have a 63a RCD Main Switch 30mA)
-----------------------------------------------------------------------------------------------------------------------
It will have 2 conduit runs in PVC in stranded cable (Method B),
1 for Lighting 8 meters
1 for Ring 20 meters
Lighting = 1.5mm (L&N) 1.0mm (Earth)
Ring = 2.5mm (L&N) 1.5mm (Earth)
Lights:- Table 4D1A
CCC = 1.5mm Method B 17.5amp
VD = 29x0.38x8/1000 = 0.08v (0.03%)
Ring:- Table 4D1A
CCC = 2.5mm Method B 24a (i see this as ok as its 20 amp per leg)
VD = 18x26x20/1000/4 = 2.34 (1%)
---------------------------------------------------------------------------------------------------
Submains
25 metre run from under stairs in house, buried under lawn to shed, to cope with a Max deman of 45amps.
Be Thermoplastic 70degree armoured 16mm 3 core cable
Using table 4D4A and B
Say im using a 50amp isolation switch (over 3 metre rule) to cope with Max demand of 45 amp
CCC = 78A
Factors = Ca 1.00
Cg 1.00
Ci 1.00
Cc 0.90 (factor for burial of cable out of OSG)
= 78a x 0.90 = 70 amp (so good enough for 45 max demand)
VD = 2.4x50x25/1000 = 3volts (1.3%)
Plus adding the submain VD of 1.3 and my final circuit for my lighting 0.03%. All in all im well within the 3% Limit.
IS THIS RIGHT. OF HAVE I MESSED UP....
Sorry about the long read...
Thanks again guys