He stated the inrush current was in excess of 2000 amps which is significantly more than 14x8 so no a type B mcb will not do for that scenario
because the inrush current if all the lights are turned in together will trip a type B mcb
He has stated that the inrush current is 8.4A, this is less than 30A (the 5x6A of a 6A type B mcb)
No, the OP clearly states 2000VA inrush, not 2000kVA.
The inrush of the lights together is 2000VA
David put your glasses on and read the post,it clearly states 8 watts per fitting and the inrush current is 2000. I think you need to learn the difference between inrush current and normal operating current.
Exactly, 2000VA not 2000A, this is quoted as the power in VA not the current in A.
2000VA is below 10A, later in the thread he clarified that the inrush current is 0.6A per fitting which gives 8.4A for the whole circuit.
Letchworth
Design of emergency lighting circuit
stuartb,
Toneyz,