HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,295
Reaction score
6,535
Location
Gloucestershire
I need to replace a Hagar RCD (model number CN284U). This is a type AC RCD and I wish to replace it with a type A.

The model number for the Type A equivalent is CNA584U.

They are both 100mA, 100A, S type.

The only difference being is that the Type A RCD is referred to as 1P + N rather than double pole. I'm getting a bit confused by the difference?
I thought the +N meant that the N is just switched off when there is a fault but doesn't actually detect the fault itself.

What is the difference between a double pole RCD and a 1P + N RCD? With both types of RCD the phase and neutral become open if a fault is detected, so it must relate to where the fault is detected (i.e phase or neutral). Or.. it is just different terminology meaning the same thing?
 
Indeed I do as taken from the quote

ADA906U 6A 30mA 6KA Type RCBO ÂŁ125.95 each

No CEF stock number unfortunately, not sure why but will ask them tomorrow when in there!
Cheers. I've brought up a picture of it from Hager and it appears to be 2 module?

In fact similar to the AD906J we get here (although it has no flylead).

 
Got to love Hager ÂŁ90 from them ÂŁ15 from elsewhere

CEF List lots of Hager rcbos as being SP+N but are definitely not.
 
Last edited:
So an update, went in today and @Risteard was indeed correct, Hager do not seem to list a single pole switch neutral or double pole in a single module size even the AFDD RCBO are single pole.
So I will be changing the lot for Fusebox as they do make a single module double pole RCBO at a very reasonable price!
 
So an update, went in today and @Risteard was indeed correct, Hager do not seem to list a single pole switch neutral or double pole in a single module size even the AFDD RCBO are single pole.
So I will be changing the lot for Fusebox as they do make a single module double pole RCBO at a very reasonable price!
Any questions like this message Hager on the whatsapp support number they are really helpful and normally reply within a few hours

+44 7778 161000
 
Got to love Hager ÂŁ90 from them ÂŁ15 from elsewhere

CEF List lots of Hager rcbos as being SP+N but are definitely not.
Yes, this was my point of confusion. I was also wondering if they were using old photo's and the side diagrams were wrong.
So an update, went in today and @Risteard was indeed correct, Hager do not seem to list a single pole switch neutral or double pole in a single module size even the AFDD RCBO are single pole.
So I will be changing the lot for Fusebox as they do make a single module double pole RCBO at a very reasonable price!
It sounds as though you were in a similar position. The install I was thinking of has a perfectly good Hager metal enclosure but with a 30ma RCD main switch. It also has 14ma of earth leakage already and there is a lot of dodgy modifications. Changing to RCBOs already looked expensive, but if they are only single pole then yes, it's Fusebox all the way.
It seems strange that mid-range brands have RCBO's that switch the neutral but Hager doesn't seem to offer one that is a single module.
 
Yes, this was my point of confusion. I was also wondering if they were using old photo's and the side diagrams were wrong.

It sounds as though you were in a similar position. The install I was thinking of has a perfectly good Hager metal enclosure but with a 30ma RCD main switch. It also has 14ma of earth leakage already and there is a lot of dodgy modifications. Changing to RCBOs already looked expensive, but if they are only single pole then yes, it's Fusebox all the way.
It seems strange that mid-range brands have RCBO's that switch the neutral but Hager doesn't seem to offer one that is a single module.

The big companies sometimes lag behind smaller ones. Look at what happened to Kodak when digital printing came along.
 
It seems strange that mid-range brands have RCBO's that switch the neutral but Hager doesn't seem to offer one that is a single module.

I've wondered about this, and similar issues, and the best I can come up with is that manufactuers concentrate their efforts on primary markets.

It may be that I'm wide of the mark here, but Crabtree, Wylex, Fusebox, SBS et all seem to primarily serve the UK market, whereas Hager, Schneider etc would primarily serve the continental European market and we get whatever suits from their respective ranges.
 
Hager, Schneider etc would primarily serve the continental European market and we get whatever suits from their respective ranges.
But Europe has been using SP + N devices for years. I've bought SP + N MCBs in France and brought them back with me, years before such things were readily available in the UK.
If anything, I would expect the UK focused suppliers to be lagging behind.
 
MCBs, yes. Never looked at RCBOs.
It's RCBOs that this thread references.

I'm not sure I'd consider either UK or Europe to be 'lagging behind' the other and consider this to be more a matter of practicality.

Manufacturers whose products are primarily aimed at UK market would struggle to sell 2 module breakers, whereas European market sees less limitations on space within domestic distribution boards.
 

Reply to Difference between 1p+N and double pole RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
977
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top