Different test results after DB change | on ElectriciansForums
Discuss Different test results after DB change in the UK Electrical Forum area at ElectriciansForums.net
Glasgow
Is it common to get different test results when upgrading a db? Basically I done an EICR in November and came back to upgrade the db and done live tests on all the circuits, but my results were quite different. Like 0.30 ohms out on one circuit
please clarify what where you testing at the time .
Are your tests after the board change?
Tested before, during initial EICR way last year. Then went back to upgrade DB this week and we live test after upgrading DB, the Zs readings on some circuits were a lot lower than they were. Meter tails were upgraded and the Ze went down by 0.11 but some circuits the Zs was 0.30 lower
It might simply be a result of re-terminating all the CPC's properly.
Does it happen to be the case that the ring final circuits are closer to original readings? In theory these will have had the CPC disconnected for fig 8 tests, so should be more recently tightened.
For other circuits it's conceivable that the CPC's weren't touched during the EICR...depending on how the tests were carried out of course.
Then again live Zs tests are notoriously variable and can be affected by electrical 'noise' easily.
Like you say could be a combination of that, and the fact the ze is went down by 0.11 since the tails have been upgraded etc
My money is on this possibility or something similar. For instance, we have recently had to carry out testing on premises that were dormant/vacant for 2 years (covid related). A number of FLi socket circuit tests were marginally higher than the regs allowed. I did wonder why the installation had been passed in the first place. However as the installation opened up for business again and sockets started to be regularly used we found on retesting some weeks later that Zs values had dropped significantly. Sometimes it can be as simple as a fine film of dust lying on the contacts
Of course if you get a high reading on a socket, the usual thing to do is to put the plug (tester plug top) in and out of the socket several times
Yes. That's what would normally be done on getting a high reading. And that's what we did on initial testing, but it did, nt bring the readings down. It was only after several weeks of the sockets been in continuous use that that there was an impact on the readings. I, m just speculating that the long dormant period led to this situation somehow
Reply to Different test results after DB change in the UK Electrical Forum area at ElectriciansForums.net
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...