S

sparkywoman

Can a Sunnyboy SB3800 inverter disconnect on a TT system fast enough to prevent injury through shock?

The installation has an RCD fitted and the inverter is connected to a 16 amp MCB.
With the inverter having simple separation, does this negate the need for an RCD to protect the cable between the inverter and the consumer unit?
 
The cable between the invertor and the CU will come under the regs and if you have buried the cable or run it under floors and it does not comply to regulations 522.6.5 and 522.6.6, then that cable will have to have additional protection by an RCd to reg 415.1.1

The RCD in the installation will ensure that the disconnection times are met.
 
As the invertor as seperation then you don't need a type B RCD.

The trouble with TT installations are that becasue of the likelyhood of having a high value Ra, and therefore not being able to achieve a Zs low enough to achieve disconnection times of a Fuse/MCB, the use of a 30mA RCD is used as additional protection.

So for PV there is a chance of fitting a 100mA RCD if you do not bury the cable or run it under the floor without the protection of regs 522.6.6 and 522.6.5. ie completey run on surface, but there woulkd be very little chance of getting away without fitting some kind of RCD.
 

Reply to Disconnection time on TT system in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
583
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top