Just received a completed test sheet from an installer on a TN system with the max permitted disconnection time column filled in for the lighting circuit and 20A heater circuit as 5secs, surely 0.4
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Disconnection times for finals in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
If it’s before 2008 then yes 16th edition disconnection times where slightly different.I have two in front of me from different contractors both have lighting at 5 secs max is this something from the 16th edition brigade
I’m not sure it’s residential street lighting that’s been discussedStreet lighting is 5s
Yes it's a 16th Edition value so has been wrong for a decade now.I have two in front of me from different contractors both have lighting at 5 secs max is this something from the 16th edition brigade