Thought I'd try out this ElectricalOM software for a new installation I'm designing. However come up with abit of an issue with the discrimination on 2 of the devices. Single phase sub feed from DB2 (60898 type c 63A 10kA) to DB3, Final circuit from DB3 (61009 30mA 32A type c 10kA RCBO)

Time v Current curve for the devices shows no discrimination for over current protection.



Any ideas or advice?






View attachment 35356

View attachment 35355

View attachment 35357
 
Thought I'd try out this ElectricalOM software for a new installation I'm designing. However come up with abit of an issue with the discrimination on 2 of the devices. Single phase sub feed from DB2 (60898 type c 63A 10kA) to DB3, Final circuit from DB3 (61009 30mA 32A type c 10kA RCBO)

Time v Current curve for the devices shows no discrimination for over current protection.



Any ideas or advice?






View attachment 35356

View attachment 35355

View attachment 35357


Hi, that's a lot of tiers, try reducing, also you need to ensure your fault current analysis is correct.
 
You nead to use an mccb board or as Dave and Lee says fuse boards to the supply distribution circuits so you can get discrimination
 

Reply to Discrimination headache!!! in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

  • Question
For anyone interested, I tested the supply side RCBO today and got a 1x I time of <130ms, so I don't believe it is a Type S. I did however have...
Replies
12
Views
3K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
656
  • Question
Exactly 😅
2 3
Replies
70
Views
7K
  • Question
To put it simply the generator cannot provide enough current to operate and mcb as fault protection. To deal with this we make use of RCDs of...
Replies
7
Views
2K
davesparks
D
Yes, seen this before too - a pertinent reminder to look twice and not assume that something actually is what it obviously should be...!
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks