Distance from red link to consumer unit

If the service head and meter are more than 3 metres away from the CU then a switch fuse should be installed after the meter
Something like that anyway, I'm knackered and have a blinding headache so can't be bothered to go and get the proper info.
Sorry mate.
 
Oh I get you now. I keep typing to slow lol. Ignore my little messages.
thanks for your help guys. His is definitely longer than 3 meters.

thanks guys. Sorry for the bad explanation!
 
If the service head and meter are more than 3 metres away from the CU then a switch fuse should be installed after the meter
Something like that anyway, I'm knackered and have a blinding headache so can't be bothered to go and get the proper info.
Sorry mate.

What's the point in that? If the cut out has a 100A fuse why then put two in sequence? Can't see the need. I only bother using a kmf if the mains is ran in 16 te and dumb it to 80A. Plus the dno supply a dual pole isolator.
 
What's the point in that? If the cut out has a 100A fuse why then put two in sequence? Can't see the need. I only bother using a kmf if the mains is ran in 16 te and dumb it to 80A. Plus the dno supply a dual pole isolator.
What? Really!?
 
The length actually varies between the different DNOs, on a recent meter move by ukpn the paperwork clearly states a maximum of 4metres.
 
What's the point in that? If the cut out has a 100A fuse why then put two in sequence? Can't see the need. I only bother using a kmf if the mains is ran in 16 te and dumb it to 80A. Plus the dno supply a dual pole isolator.

The point is that the DNO specify a maximum length of tails which are allowed before the consumer must provide their own protective device. Generally this is 3 metres but some allow 4 and others 2.5
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Nicholas,
Last reply from
LankyWill,
Replies
31
Views
10,355

Advert

Back
Top