S

Spearmint

Thought I'd throw this out there and see what others think. We're working working on a boiler house and storage room separated by an internal wall which is all a separate building to the house. Supply is coming from the house into the new building as a sub main and contains...

2 x 32A MCB ring mains, one for sockets around the inside of the boiler house and the other for the inside of the storage room.

1 x 16A MCB to an immersion of unknown rating (hasn't been ordered yet).

2 x 6A MCB - one for the lighting for both rooms and the other is for the boiler + stats etc.

...all this from a 40A incomer (I'm unsure what the house supply is, presuming 100A).

I'm not part of the CU install, just had a nosy on how the others we're getting on but tried practicing working out diversity after getting a good look at the DB and I work it out to be over the 40A on the incomer.

RFCs: 32A @ 100% + 32A @ 40% = 32A + 12.8A = 44.8A

Have to assume full 16A for the immersion as it isn't on site yet, no diversity allowed so: 44.8A + 16A = 60.8A so far.

Lights: 6 x 100W = 600W / 230V = 2.6A x 66% = 1.7A - 62.5A so far.

Boiler: Unknown load, all controls though so barely anything I imagine, have left this out.

So even after leaving the boiler circuit out I'm at 62.5A on a 40A incomer.

I'm I missing something? Surely this can't be right?
 
So all the earache you gave me was worth it, Glenn.

Did you do an averaged KWHr reading? Hope you did because that would blow holes in any diversity calculations.
well i had gone down with the power quality analyser to do just that....but found out i couldn`t get the CT ring into the dis-board enough to get an accurate reading (conductor to be a min of 25mm from edge of CT ring)...so that was a no goer....

went with the clamp as best i could do....but there will be other opportunities to get the power analyser out....
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Diversity
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Spearmint,
Last reply from
GLENNSPARK,
Replies
15
Views
2,108

Advert

TrueNAS JBOD Storage Server

Back
Top