Spearmint

Thought I'd throw this out there and see what others think. We're working working on a boiler house and storage room separated by an internal wall which is all a separate building to the house. Supply is coming from the house into the new building as a sub main and contains...

2 x 32A MCB ring mains, one for sockets around the inside of the boiler house and the other for the inside of the storage room.

1 x 16A MCB to an immersion of unknown rating (hasn't been ordered yet).

2 x 6A MCB - one for the lighting for both rooms and the other is for the boiler + stats etc.

...all this from a 40A incomer (I'm unsure what the house supply is, presuming 100A).

I'm not part of the CU install, just had a nosy on how the others we're getting on but tried practicing working out diversity after getting a good look at the DB and I work it out to be over the 40A on the incomer.

RFCs: 32A @ 100% + 32A @ 40% = 32A + 12.8A = 44.8A

Have to assume full 16A for the immersion as it isn't on site yet, no diversity allowed so: 44.8A + 16A = 60.8A so far.

Lights: 6 x 100W = 600W / 230V = 2.6A x 66% = 1.7A - 62.5A so far.

Boiler: Unknown load, all controls though so barely anything I imagine, have left this out.

So even after leaving the boiler circuit out I'm at 62.5A on a 40A incomer.

I'm I missing something? Surely this can't be right?
 
So all the earache you gave me was worth it, Glenn.

Did you do an averaged KWHr reading? Hope you did because that would blow holes in any diversity calculations.
well i had gone down with the power quality analyser to do just that....but found out i couldn`t get the CT ring into the dis-board enough to get an accurate reading (conductor to be a min of 25mm from edge of CT ring)...so that was a no goer....

went with the clamp as best i could do....but there will be other opportunities to get the power analyser out....
 

Reply to Diversity in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
722
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top