Engineer54
Metal containment systems have been extensively used for far more years than i've been around. It has long proved itself as providing both sound mechanical protection and as a sound electrical earthing (cpc). No such thing as a spindly metal conduit system!!
I can show a multi factory site built from the 50's, with extensive metal containment systems that have Zs values that even to this day, don't come even close to max values... If that's not deemed as being reliable then i don't know what is!!
The problem with metal containment is that these days far too many electricians don't have any experience of installing it, they are far more likely to be seen hacking and butchering it to enable them to run T&E or SWA or the like!!
Every major project that i've been involved with, metal containment has been the predominant means of electrical installation without a single separate CPC conductor in sight!! All our metal containment systems are subjected to high current (25A) ohm meters sectional tests, and believe me you can't hide any weak connections with those things. Metal containment systems erected/installed and tested by experienced operatives will last for decades. As a system it's second to None, and ill stand by that statement till the day i die!!
I can show a multi factory site built from the 50's, with extensive metal containment systems that have Zs values that even to this day, don't come even close to max values... If that's not deemed as being reliable then i don't know what is!!
The problem with metal containment is that these days far too many electricians don't have any experience of installing it, they are far more likely to be seen hacking and butchering it to enable them to run T&E or SWA or the like!!
Every major project that i've been involved with, metal containment has been the predominant means of electrical installation without a single separate CPC conductor in sight!! All our metal containment systems are subjected to high current (25A) ohm meters sectional tests, and believe me you can't hide any weak connections with those things. Metal containment systems erected/installed and tested by experienced operatives will last for decades. As a system it's second to None, and ill stand by that statement till the day i die!!