You are talking about the DNO supply here and not a 95mm from your local sub DB? If the 95mm is to the DNO cut-out then I would imagine if THEY needed to, they would put 300Amp fuses in if it saved them money. They're interpretation of current carrying capacities and BS7671 guide for current carrying capacities are two wildly different things!
Here's the conversation;
You: I need a 200A supply
DNO:eek:k, well we need to do some calcs, more calcs, alter supply characteristics etc etc that will cost you ÂŁkkkkkk and our engineer will be along to replace 150A fuses with 200A fuses.

As has been previously posted, this will come down to generator costs outweighing DNO fuse replacement costs.

Are you implying here that the installation of a generator and it's overall running costs is going to be a cost effective solution over the DNO's charges for uprating the supply fuses??

If you are, then you obviously have no experience of running prime power generators....
 
Hi guys, thanks for all your responses. Here is a little bit more detail for those of you who have asked some questions of my original posting. I also note a number of criticisms about that I should find an electrician (which we will) and that when I turn we turn the lights on my electricity usage might go up (yep, understand that). A number of years ago, the club upgraded it's supply into the premises when it installed a new hockey pitch with a plan to provide enough power availability for floodlighting at a point in the future. For a variety of reasons the floodlight project was never done and here we are a number of years later looking at it again. I had an initial enquiry with the DNO some months back before I really knew what I was doing and I sent some photographs of our installation which terminates into a "Lucy Oxford 4MC200 Insulated Cutout" and it was them who told me I had a 95mm cable supplying the building and I also know from historic notes that the supply is fused at 150 amps (DNO fuses) in our premises inside this cutout. The problem is hockey pitch lighting has moved on and the previous power installation may no longer be enough so all I am really trying to establish is whether it might be possible to pull more capacity from the existing supply cable with just a fuse upgrade (I appreciate this assumes substation capacity availability) and I think from the responses I have got they indicate this might be possible without a cable change. Thanks to everyone for the help and apologies for the slightly vague approach.
 
If your original design was a few years ago it was presumably planned with metal halide lamps, the use of high quality LED lighting could reduce your energy consumption by about 10-30% and so may negate the need for an upgrade. The additional initial cost of which could be offset against the need not to upgrade fuses, and the reduced running costs would be significant from an ongoing point of view.
 
You really need to know what the loading is going to be for this proposed hockey pitch lighting. So a design needs to be put forward and accepted, that meets whatever association governs hockey these days. (if this hockey pitch is to meet official minimum standards) Only then will you have loading figures that are going to mean anything as regards assessing if your present supply is adequate for it's intended purpose!!

So do you have a suitable club pitch lighting design in place as yet or not??
 
Hi RichardBurns, the supply over to our pavilion was put in to handle up to 63 amps per phase as the requirement, 15 years ago for hockey pitch lighting was much lower than it is today so we definitely don't have enough capacity in the existing cable but thanks for the suggestion.
 
Hi Engineer54, I have a full lighting design from Philips, and I know the power requirements for both designs, 350/500 lux and for the lamps that are required so I'm well on my way with regards to that side of things, this power side is a steep learning curve but I'm getting there slowly. The problem with this sort of thing is the power side of things might make it or break it depending on availability of power and the cost of any change on the DNO side.
 
Could someone answer me this. I'd just like to point out I'm enquiring so I can understand this whole thing better, I am fully aware this will all have to be re-done by suitable electricians and such like but getting good advice in the very early stages of grant funded applications is quite difficult hence why I'm leaning on a potentially helpful sole on these forums at the current time. The total power requirements of our project would be 28 x 2119w lamps, where each lamp is connected to 2x power phases. This results in a total load of 59.33 KW to achieve 500 lux lighting levels. We also have an option for 350 lux lighting levels using 20 lamps of the same type giving a total load of 42.38 KW. What I would like to know is what current per phase is required to support this project and what would this also be in KVA. If I have not supplied enough information then please let me know.
 
As R, Burns has stated above LED light fitting may be an option, but in any case a reappraisal of the overall lighting design for your pitch should be conducted. Things change over a 15 year period, especially as the trend these days is more and more towards lamp efficiencies etc...
 
Hi, sorry I should have been more clear, the lighting design is brand new and based on modern standards. I've investigated LED lighting but it's not a viable option which would have been great in power terms. We're talking about lighting a 100m x 50m space to 500 lux and from the people I have spoken to who do this for a living, LED is not quite there yet.
 
Aha, so Scottish Power got back to me today we are on a 95mm waveform cable and this can be moved to 200 amp fuses by just changing the fuses. 246.77 + VAT, great result. The one thing it does state is our requirements, one of them being "Provide interconnecting cable of an approved type between the termination equipment and your main switch gear. The cable size shall not be less than 25sq mm copper and must not exceed two metres in length". Does 25mm square sound enough for 200 amps per phase?
 
Your getting confused here the 25mm is the minimum by regulation not the size they are suggesting, you are at a stage now where you really need to get a competent Electrician on board with experience in commercial and industrial circuit design, ensure that this is there field and you don't get a souped up domestic electrician out of his comfort zone, there are too many questions to ask and info you need to provide us, a simple missed bit of info can be vital to a correct install.

Comments regarding discrimination earlier between consumer and DNO are usually not an issue as long as your fuses are less than or equal to theirs... normally we fit type II fuses where the DNO will fit type III or IV.

As the incoming N on the DNO will be possibly combined with Earth you will need an Electrician to establish that any consumer cabling upgrade is correctly done regarding the Earthing system

The original question seems to have been answered by yourself through enquiry but TBH this was the only way it could have been done with liaising with DNO as you will have been allotted a set KVA for which you will have a standing charge, if your supply was upgraded yrs ago without the alloted KVA set it could be the case they could turn around and say the supply upgrade isn't available and a very high cost of a new sub-station may have been on the cards, if you were marked up for your alloted KVA when supply was upgraded then you have been paying over the odds for your standing charge but safe guarding your KVA reserve within the local network.. this seems to be the case or you have been lucky that your requirements were still available in the local network.

We could ask you question after question and still miss crucial info as we would need to see the physical set up. I can appreciate you questioning for groundwork but this will all be normally done by your contracted electrician so don't get too involved or misunderstood info or incorrect spec's you provide may be costly and we aint talking a few quid here... we could be talking the whole cost of the install down the drain... ive seen this happen before.
 
and what did you downsize it to ?
because to achieve fault discrimination with 200A bs88 fuses , youre going to be limited to around 130-140A as the maximum sized protective devices on the consumer side.
which makes it pointless getting a 200A supply in the first place.
To be honest, I left them in. Never had any problems.
 
Modern daylight robbery being practiced.... ÂŁ250+ VAT to change out 3 cartridge service fuses. Now that's what you call a profit margin!! lol!!
 

Reply to DNO Supply Question in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I like the plan. Best of luck.
Replies
6
Views
464
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
511

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top