The relevant regulations are I think as follows:

BS 7671 513.1: cable joints must be accessible except where allowed by 526.3

which is covered by ...

BS 7671 526.3 (iv) joints made by welding, soldering, brazing or compression (which covers crimped connections)

So far so good. But:

526.5 (iii) Every termination and joint shall be in an enclosure partially formed or completed with non-combustible material.

This I think does not cover a choc box which is as far as I can make out is made of polyproplyne which is combustible.

Am I missing something?

I know you will all say I should use Wago connectors in a Wago box which is obviously correct, but I want to know how I should treat existing inaccessible crimped connections in a choc box in an inspection.
 
later ...

I found the specification for a Greenbrook CHOC30A which says it conforms To BS EN60670-22, which is the standard for "Boxes and enclosures for electrical accessories for household and similar fixed electrical installations". So these choc boxes comply with BS 7671 526.5 (i) "A suitable accessory complying with the appropriate standard", and are therefore actually OK.
 

Reply to Do crimped connections in a choc box in an inaccesssible location comply with regulations? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I was hoping so. What rules apply here?
Replies
8
Views
5K
  • Question
Two ways for me either Wago's or Hager Face Plates which have a Neutral connection built in to switch plate.
Replies
14
Views
2K
C
J
TysSome infopical questions asked by installers Should WAGO connectors be used in an enclosure? In order to comply with the requirements of the...
Replies
22
Views
24K
nickblake
N
E
Welcome @Geraldine you may be better off starting a new thread with more detail as Edd is no longer a forum member.
Replies
60
Views
80K
C
You have a valid point Tony but had this member not posted in this thread then I probably wouldn't have had the pleasure of reading it. Very...
Replies
66
Views
33K
1shortcircuit
1

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks