What are peoples thoughts on this, should socket outlets in the general public areas be RCD/RCBO protected? I believe they do and have put them down as a C2 on a recent EICR but recently got a phone call to say it's a C3!
 
It doesn't matter whether it excuses compliance with current Regulations.
The fact remains that the IET are never going to say that a situation which was deemed safe in previous editions is now unsafe. (The legal ramifications would be enormous.)

BS7671 requires us to make observation on non-compliances which may give rise to danger.
If the Regs. do not consider a non-compliance which complied at the time of construction to be unsafe, how can you then state the situation is potentially dangerous?
 
Looks like the thunder has arrived.
At least here it has.

[ElectriciansForums.net] Do socket outlets in a Pub need to be RCD/RCBO protected!
not here!

[ElectriciansForums.net] Do socket outlets in a Pub need to be RCD/RCBO protected!
 
It doesn't matter whether it excuses compliance with current Regulations.
The fact remains that the IET are never going to say that a situation which was deemed safe in previous editions is now unsafe. (The legal ramifications would be enormous.)

BS7671 requires us to make observation on non-compliances which may give rise to danger.
If the Regs. do not consider a non-compliance which complied at the time of construction to be unsafe, how can you then state the situation is potentially dangerous?

Well they have, there are many things which were once required by the regulations which are no longer compliant, fused neutrals being one example.

If the regs do not now consider an item which complied at the time to be unsafe now then it is not unsafe, however if the regulations do now consider it to be unsafe then it should be coded.

Fused neutrals complied with a previous edition.
Unfused supplies complied with a previous edition.
Bare conductors on cleats complied with a previous edition.
Green being used for L3 complied with a previous edition.
Open fronted switchgear complied with a previous edition.
Bare conductors encased in a wooden moulding complied with a previous edition.

The point is that if an item does not comply with current regulations and it is immediately dangerous then it is a C1
If an item does not comply with current regulations and is potentially dangerous it is a C2
If an item does not comply with current regulations and an improvement can be recommended for safety based on current regulations then it is a C3
 
What editions permitted bare conductors on cleats and in wooden containment? Single insulated conductors yes, but bare conductors?

Off the top of my head I think it's in the 9th edition that I've seen it.
Just to clarify I'm talking about bare conductors on cleats which are not placed out of reach or behind barriers etc as is now required.
 
Hmmm.
Says bare conductors on cleats which is still allowed.
Then says bare conductors encased in wooden mouldings.
As far as I am aware, wooden backed accessories and wooden containment are still allowed.
Not sure about the bare conductors encased in wooden mouldings?
 
If an installation has been installed to a previous addition of BS7671 eg 15th/16th and still complies with that edition should not make the installation warrant a C1 (danger present .risk of injury immediate action required ) or C2 (potentially dangerous) the standard of additional safety of which electrical installations are installed to has changed/improved .Other regulations eg H & S acts may come into play and require RCD protection. I can't see what Part P has to do with a EICR however if I am correct it comes into play if certain work is undertaken when the domestic and business premises share the same meter.
for what reason
 

Reply to Do socket outlets in a Pub need to be RCD/RCBO protected! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
444
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
2
Replies
17
Views
4K
  • Question
ok cheers for the help lads
Replies
7
Views
719

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top