warrington
What are peoples thoughts on this, should socket outlets in the general public areas be RCD/RCBO protected? I believe they do and have put them down as a C2 on a recent EICR but recently got a phone call to say it's a C3!
To be honest I would C3 sockets domestically say for upstairs were sockets are generally not likely to be used for supplying outdoor equipment yet they can be multiple USB type so I don't see any relevance.
This is not domestic of course
We have the same issue with outdoor light fittings not being mechanically protected and wanting to put them on rcd/RCBO protection, it always gets knocked back.
I did some commercial buildings (EICR) and this is a very grey area. Not one CPS scheme can agree on this there is no coherent standard to work from and it is very much up to you the man on site to make your judgement. There were only about 10% RCD protected units/offices. In the end we recorded C3 for all the lack of RCD contingent upon the CEO agreeing to put in place a program of upgrades where RCD was lacking. It is a very contentious area at the moment, I fear it will get worse with the 18th. We did a general risk assessment for the lack of RCDs and it was noted that they had a very good system of checking regularly equipment, no history of accidents and maintenance was really good and conscientious. If it had lacked these factors we would definitely have recorded C2 for a lot of the lack of RCDs. I just wonder what the general condition of the pub was and maintenance etc. This would sway my decision accordingly. So what if you put it in writing and kept the email copy?
Told them that and had many an argument over it, he changes the codings without us knowing it, we found out by one of the lads in the office telling us.
Well that's nice of him to tell you and your guys.
It's poor management skills really and if he has issues with any coding going on he should have a talk about it to all operatives under his management/supervision
That makes no sense at all, of course you've been knocked back.
An RCD does not provide any sort of mechanical protection, if mechanical protection is required then you need to install mechanical protection to rectify it.
Reply to Do socket outlets in a Pub need to be RCD/RCBO protected! in the UK Electrical Forum area at ElectriciansForums.net
Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
4K
ok cheers for the help lads