What are peoples thoughts on this, should socket outlets in the general public areas be RCD/RCBO protected? I believe they do and have put them down as a C2 on a recent EICR but recently got a phone call to say it's a C3!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Do socket outlets in a Pub need to be RCD/RCBO protected! in the UK Electrical Forum area at ElectriciansForums.net
I would be c2What are peoples thoughts on this, should socket outlets in the general public areas be RCD/RCBO protected? I believe they do and have put them down as a C2 on a recent EICR but recently got a phone call to say it's a C3!
It's a bit out of date buzz at it still refers to skilled and instructed persons 2008
Well of course that has been updated now so that Skilled persons bit has been removed.please read.
To be honest I would C3 sockets domestically say for upstairs were sockets are generally not likely to be used for supplying outdoor equipment yet they can be multiple USB type so I don't see any relevance.The cables supplying them are less than 50 mm depth and I've started seeing a lot more people charging phones, laptops or tablets for kids. Personally I think there a C2 because of the above and more and more sites are starting to change there sockets for the ones with the USB charge outlets.
It was the QS and Electrical ManagerYeh but still would like to know who the hell rung you and told you your report was wrong, what do they know you don't?