Hi all

Replacing a consumer unit and I always upgrade the tails from the meter to 25mm.

However, the run is an absolute nightmare for a flat im doing a the meter is in the communal hallway.

I'm assuming they have to be upgraded if changing consumer unit?
 
The onsite guide recomends you do however remember that is just a guide, If the tails are in good condition and are covered by the main service fuse then id leave them in place. IE 100a gets 25mm

I usually allways fit new tails however if as you say its a pig of a job then providing that are large enough and in good nick then they can stay
 
I agree with wirepuller and bigbaddave.

If it's unpracticable to replace the tails then don't do it - providing they're adequate for the load.
 
The onsite guide is purely a "guide" and is mainly aimed at new builds.

Just imagine the size of the OSG guide if it covered all eventualities!!
 
The answer is NO, it's like asking do you have to replace the consumer unit if you are replacing the tails, why are you assuming they have to be upgraded? and why do you always replace existing tails with 25mm?
Hi all

Replacing a consumer unit and I always upgrade the tails from the meter to 25mm.

However, the run is an absolute nightmare for a flat im doing a the meter is in the communal hallway.

I'm assuming they have to be upgraded if changing consumer unit?
 

Reply to Do tails HAVE to be upgraded? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
463
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
744
Ah my mistake - apologies. I have something more or less like this wylex unit and the flappy plastic cover has got a broken pin so won't stay one...
Replies
4
Views
285

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top