HappyHippyDad

-
Esteemed
Arms
Supporter
I can't find any really up to date threads on whether we have to fit AFDD's.

I am specifically talking about in a domestic premise. I can see that 421.1.7 shows where an AFDD HAS to be fitted (i.e in one of the 4 bullet points), but then it says below ( the bullet points) it is 'recommended' that AFDD's are fitted in ALL premises for socket outlets.

The Napit Webinar (02/11/2022) kind of skips lightly over this point. At 11 mins and 25 seconds he says something along the lines of 'it is up to the designer whether to use the recommendation of using AFDD's'.

It clearly is not mandatory otherwise the reg would not state the 4 examples of where it actually is mandatory. So it is actually optional, but there isn't any criteria given to help you decide whether or not you should fit one.

Does anyone have any clarification on this?
 
Ive got a EICR to do today that requires measuring the building height ( floors ) to see if it come under HRRB regs and needs AFD’s

They better hope its under 18m !! Otherwise its 5x new AFD and thats not cheap !
 
I live in a timber clad and old oak barn conversion. It has been fully rewired to a high standard. Because of multiple buildings, we have multiple CUs, all Hager. We recently decided to fit AFDDs to all areas where we have any kind of fire risk concern and had no difficulty getting them via our trade accounts. What is interesting is the resistance to using them which I think is largely driven by cost. We paid £102 each, plus fitting and testing and some other necessary changes due to CU space. This is not a trivial sum for AFDD multiples in domestic properties. I am a developer, not a qualified electrician, though I am familiar with the regs. If the regulatory authorities think AFDDs will materially reduce fire risk then having vague wording like "recommended" is ridiculous. Eventually insurance companies will drive this. I specify them in developments now. They make sense to me.
NOT HAGER my god anything but them....they dont even trip when they are nearly on fire
 
Ive got a EICR to do today that requires measuring the building height ( floors ) to see if it come under HRRB regs and needs AFD’s

They better hope its under 18m !! Otherwise its 5x new AFD and thats not cheap !

Not necessarily 5x new AFDDs, that would only be a C3 and so a recommendation, not a requirement.
 
I've only watched the first of the videos, not a good showing to not detect some serious arcing.
I've seen the result of parallel arcing at church. We had a fuse blowing intermittently but couldn't find any cause. It was only when someone mentioned a socjet not working that I found a length of T&E going through a 3ft thick wall where the mice had been at it - and about 6" was burned away from arcing, just like the test the video showed the Hager device not detecting.
 

Reply to the thread, titled "Do we have to fit AFDD's in domestic installations?" which is posted in Domestic Electrician Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top