I can't find any really up to date threads on whether we have to fit AFDD's.

I am specifically talking about in a domestic premise. I can see that 421.1.7 shows where an AFDD HAS to be fitted (i.e in one of the 4 bullet points), but then it says below ( the bullet points) it is 'recommended' that AFDD's are fitted in ALL premises for socket outlets.

The Napit Webinar (02/11/2022) kind of skips lightly over this point. At 11 mins and 25 seconds he says something along the lines of 'it is up to the designer whether to use the recommendation of using AFDD's'.

It clearly is not mandatory otherwise the reg would not state the 4 examples of where it actually is mandatory. So it is actually optional, but there isn't any criteria given to help you decide whether or not you should fit one.

Does anyone have any clarification on this?
 
You have answered your own question as such.
Yes, they are recommended but not compulsory. If, however, you are in a house where someone perhaps has a disability/mobility issues, you may think it prudent to fit AFDDs to help prevent the risk of fire.
It really comes down to you as the designer and the customer because they have to pay for it.
 
You have answered your own question as such.
Yes, they are recommended but not compulsory. If, however, you are in a house where someone perhaps has a disability/mobility issues, you may think it prudent to fit AFDDs to help prevent the risk of fire.
It really comes down to you as the designer and the customer because they have to pay for it.
The bit I'm kind of getting at is the criteria for fitting AFDD's.

You have used some of your own judgement to decide that you 'may' fit an AFDD in a house where the occupier has a disability/mobility issue.

You haven't said you WILL fit one in the above scenario, just that you 'may'. So you've made a judgement in the first place that someone with a disability needs one, but not definitely.

What type of disability issue? What kind of mobility issue? Severity of disability etc. We'll need to have a bit of medical knowledge to make those decisions.

The point I'm getting at is there isn't any criteria. It's just a judgement call. It doesn't seem to be a judgement call that is based on any electrical knowledge. It is based on hundreds of other factors.... mobility, disability, what the house is made of, existing condition of house, age of wiring, does the house have rodents and many, many more.
 
You're right. There is no exact criteria. Essentially it is up to you as the designer to decide if it is necessary in any given circumstance. This is just my take on it though. I may well have it wrong.
The BBB at it's vague best.
 
Yea its a bit crap, because if we go against the recommendation, and something goes wrong, where do we stand. Why did we not fit something recommended by the more knowledgeable iet?
 
They are mandatory on circuits containing socket-outlets in HRRBs (higher risk residential buildings). They are not mandatory generally in domestic premises. A recommendation is simply that - a recommendation. It does not compel you.
 
Who knows!!!!

Probably the worst wording in the whole of the regulations.

Basically AFDD is Recommended, so it is tempting to believe you don't have to.

However the regulations define recommended, as meaning that this is the option they advise in order to achieve the protection required (see page 18) (paraphrased to match this aspect).

So you don't HAVE to use AFDD to provide protection for arc faults, you could use something else. But ultimately you do need to do something to protect against arc faults. The regulations recommend AFDD as the tool to use.

The thing is there is nothing else!

I think they added "recommended" thinking about the traditional use of the word, unaware or forgetting that it had actually been qualified somewhat specifically in the regulations.

Bit of a mess in my opinion.
 
The bit I'm kind of getting at is the criteria for fitting AFDD's.

AFDDs are currently rare and very expensive, the IET know that they won't get fitted by a lot of jobbing electricians doing one-off jobs, rewires, CU changes etc. They also know that for those kind of jobs customers aren't going to accept the cost and will often choose the electrician who ignores the rule if they were to make them mandatory.

The only way the price is going to come down is by AFDDs becoming more commonly used and demand increasing.

By making it a recommendation they know that the people designing/specifying large scale domestic installation jobs, like whole new build estates, will specify AFDDs.
Housing associations, councils, listed buildings people will also start jumping on the band wagon and specify them.

This way the demand will increase and so drive the price down.

In the future we will see them become mandatory everywhere, but not until it is reasonably possible.

Now the cynic in me also wonders if making this a recommendation is also a way of dodging the blame if AFDDs do prove to be as troublesome and unreliable as some think they will be.
 
Adding any electronic circuitry is going to make the installation less reliable in terms of nuisance tripping and failure of the device itself.

Extract from some research into AFDDs:

If it is assumed that some amount of Electrically Initiated Fires (EIF) are initiated by arc-faults, there is still
significant doubt whether the introduction of AFDDs will effectively manage that risk. Empirical and
documentary evidence affirms this, for example, the tripping thresholds stated in the AFDD product standard are higher than the levels at which arc-faults could still cause ignition.

Any benefit brought by AFDDs is not sufficiently evidenced, the incidence rate of AFDD-detectible arc-faults is unknown. The primary disbenefit to AFDD technology is cost, which in a circumstance where AFDDs become mandated, may have the unintended consequence of delaying recommended improvement works.

An additional unintended consequence might be the distraction from more effective prevention of EIF, which principally would involve measures to reduce the general incidence of electrical faults through regular testing and inspection.
 
I live in a timber clad and old oak barn conversion. It has been fully rewired to a high standard. Because of multiple buildings, we have multiple CUs, all Hager. We recently decided to fit AFDDs to all areas where we have any kind of fire risk concern and had no difficulty getting them via our trade accounts. What is interesting is the resistance to using them which I think is largely driven by cost. We paid £102 each, plus fitting and testing and some other necessary changes due to CU space. This is not a trivial sum for AFDD multiples in domestic properties. I am a developer, not a qualified electrician, though I am familiar with the regs. If the regulatory authorities think AFDDs will materially reduce fire risk then having vague wording like "recommended" is ridiculous. Eventually insurance companies will drive this. I specify them in developments now. They make sense to me.
 
Cost is one consideration, but their effectiveness in detecting different types of arc is another valid concern. In the US, the use of these devices has been controversial due to considerable issues with them -what I don't know is whether those issues are down to arc fault detection devices or widespread problems with fixed wiring and these devices functioning as intended.
 
Others have said most that needs to be said about this, but I guess for non-mandatory situations you need to consider how you might try, however vaguely, to quantify the risk elements that might justify fitting AFDD (or not):
  • Is the circuit likely to have equipment of questionable reliability attached? For example, some rental or public sockets would be riskier than a commercial setting with PAT checked stuff, or a newer home with new equipment in use.
  • Is the building construction one that is more likely to burn or have a high speed of fire propagation? So old wood buildings or conversions, or places where flammable material might be stored could be factors to apply.
  • In the event of a fire, are there unusually big consequences? So a building with folks of limited mobility and/or mental capacity to respond a factor in term of risk-to-life, a historic building or museum might be a factor in terms of loss of irreplaceable material, or high-rise where fire-fighting could be difficult to deploy, etc.
On the flip-side, there might be situations where AFDD are a poor technical fit and are not justified by the above, so places with power tools and similar in use where arcing is likely to trip them.

How you actually weigh up the above is not something I can answer! But if you have no specific reasons to say there is above-average risk, then you could argue that they are offering a negligible advantage and the cost of fitting would be better spent by the customer on linked fire alarms (if not already present) or fire extinguishers, etc.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Do we have to fit AFDD's in domestic installations?
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
42
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Simon47,
Replies
42
Views
8,021

Advert

Back
Top