Darkwood

Right ... Just been nudged to set this up by Paul.M and sounds a good idea following recent threads I've done in the Arms..

Rules....No Offensive material... edit if required before posting as this is the public arena.
Anything to do with the trade or in and around it ...H&S pic's welcome.

[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!

I've posted this a few times and this is at a mates house following a kitchen refirb several yrs ago. :eek:mg_smile:

[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!
 
Needless to say, the list of things right in that house would be shorter than that of what's wrong. Got to 30 observations then gave up filling in the cert to be honest. Socket outlets in the bathrooms, very little to no earth sleeving used, bad connections at most accessories inspected, jointboxes everywhere, CPCs used as strappers, no earth continuity on half a dozen circuits including socket circuits, outside jointbox which comprised a pattress & blank plate. Plus a bonus "hybrid" circuit which left the board as a 10mm T&E, was immediately joined to 16mm T&E beside the board (see 1st pic). Never did find the joint at the other end but that circuit ended up supplying most of the kitchen sockets, the boiler, oven & hob. (I was assured by the tenant it was a joint and not another consumer unit, he couldn't remember what part of the wall it was hidden in though!)

Bit of a weird setup with long-term tenant who's done alot of work to the property themselves over the years as a return favour for a very low rental rate and a landlord who recently inherited the house. Report is definitely not going to go down well.
 
I recently had one very similar.
A pre work survey for a board change turned into a quote for a rewire in about an hour.
Also had multiple unused live cables taped up and left floating about behind plasterboard and or in ceiling space..

Fortunately the customer was really keen to get the rewire done once made aware.
 
Currently doing an EICR as been asked to provide a second opinion. This place allegedly passed the last inspection but the estate agent and landlord weren’t happy.

There are a sh!t loads of faults. But this one I found whilst tracing a cable run from an unidentified circuit. ??‍♂️

In the words of Del. ‘No way, no way a qualified electrician did that’! ?

[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!
 
Yep unfortunately it is. It’s part of the light circuit!!

So far I have:

6 x C1’s including the one posted.
13 x C2’s
2 x FI’s

I’ve still got a fair way to go but safe to say the landlord is not happy with the previous inspection. ?

The letting agency need to be aware of this. I would point out to them that whoever is doing their EICRs is blatantly leaving them open to future court cases.
 
Yep unfortunately it is. It’s part of the light circuit!!

So far I have:

6 x C1’s including the one posted.
13 x C2’s
2 x FI’s

I’ve still got a fair way to go but safe to say the landlord is not happy with the previous inspection. ?
Must have been one of those new 'drive by' inspections that I keep reading about...
 
The letting agency need to be aware of this. I would point out to them that whoever is doing their EICRs is blatantly leaving them open to future court cases.

Must have been one of those new 'drive by' inspections that I keep reading about...

They have already given them a ‘don’t call us we‘ll call you!’ They had their concerns hence asking me to give a second opinion. When I saw the consumer unit was fed direct from the meter via 16mm T&E and it was on a 100A cutout I knew things weren’t going to go well. I phoned the estate agent at that point and said I had only opened the meter cabinet and already graded it unsatisfactory as 16mm T&E is rated at 85A at best. It may well have a 80A fuse inside the cutout. But as I cant pull it to check then I have to go by what it says on the carrier. I calculated the max demand using diversity to be 86.8A so I doubt it’s on a 80a fuse.

Plus it’s a TN-C-S system and the main earth is the 6mm CPC from the 16mm T&E, that and there are exposed single insulated cores going into to the meter.

I guess the last inspection was by ‘Bodgeit & Scarper’ ?
 
They have already given them a ‘don’t call us we‘ll call you!’ They had their concerns hence asking me to give a second opinion. When I saw the consumer unit was fed direct from the meter via 16mm T&E and it was on a 100A cutout I knew things weren’t going to go well. I phoned the estate agent at that point and said I had only opened the meter cabinet and already graded it unsatisfactory as 16mm T&E is rated at 85A at best. It may well have a 80A fuse inside the cutout. But as I cant pull it to check then I have to go by what it says on the carrier. I calculated the max demand using diversity to be 86.8A so I doubt it’s on a 80a fuse.

Plus it’s a TN-C-S system and the main earth is the 6mm CPC from the 16mm T&E, that and there are exposed single insulated cores going into to the meter.

I guess the last inspection was by ‘Bodgeit & Scarper’ ?

Could well be an 80A fuse - the house won't draw anywhere near that figure.
 

Reply to Dodgy trade pictures for your amusement! - 1 Million Views! in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top