Right ... Just been nudged to set this up by Paul.M and sounds a good idea following recent threads I've done in the Arms..

Rules....No Offensive material... edit if required before posting as this is the public arena.
Anything to do with the trade or in and around it ...H&S pic's welcome.

Beware plumbers!!!.jpg

I've posted this a few times and this is at a mates house following a kitchen refirb several yrs ago. :omg_smile:

Beware plumbers!!!.jpg
 
I thought G/Y was explicitly only for CPC use?

Edit: Yes, see 514.4.2
Is this the part of that reg you mean?:

Single-core cables identified by green-and-yellow throughout their length shall only be used as a protective conductor and shall not be overmarked at their terminations, except as permitted by Regulation 514.4.3.

I read this as applying to singles only, and assume that G/Y cores of multicore cables can be oversleeved and repurposed
 
Had an emergency call out this morning, a builder who’s installing a drain chopped through the SWA supplying the garden shed. Knocked out half the supply to the street, DNO engineer arrived promptly and changed one of the fuses down the sub station. Circuit isolated and power restored.

In the builder’s defence, the cable wasn’t buried the correct depth and was just beneath the slabs, but you can clearly see where the cable enters the ground so he should have checked prior to cutting.

FF29E498-829F-4A55-A17D-ED9DAC145653.jpeg
 
Had an emergency call out this morning, a builder who’s installing a drain chopped through the SWA supplying the garden shed. Knocked out half the supply to the street, DNO engineer arrived promptly and changed one of the fuses down the sub station. Circuit isolated and power restored.
Are you sure it is a shed supply from the house? Sounds more like chopping the concentric feeding the house to do that!
 
Are you sure it is a shed supply from the house? Sounds more like chopping the concentric feeding the house to do that!

Yes as I carried out R1R2 and IR testing on the circuit when i’d disconnected it from the board.

Also carried out a Ze, PFC and some RCD testing on the installation once power was restored and all was good.

DNO engineer said he don’t know why the fuse blew down the substation as over 300amps, but he thinks it could have been weakened from other faults in the area.
 
Good low resistance fault, live to N and PE
bet the steel disk on his diamond wheel looks pretty.

Yep, the IR results weren't pretty either- 0.02, 0.01 & 0.36 MOhm.

He goes, "i think i've only knicked it"

i said, you've done a little bit more than that mate, you're lucky that RCD kicked in when it did. 😂
 

Reply to the thread, titled "Dodgy trade pictures for your amusement! - 1 Million Views!" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top