Back to a pub kitchen I worked in a month or so back. His fryers have overheated the sockets.

It’s a duel fryer… 2 x 3kW I recall, and I told him to plug them into different double sockets.
All good.

This is what met me this morning….

[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!
[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!


13A fuse is welded into the plug, and has melted the front of the socket. Backside of socket has no signs of heat damage.

Replaced the socket and plug, but it’s likely to happen again.

13A plug should be fine for the fryer but it must be the duration that it’s on for during a weekend shift…
Or could it be down to hot oil splashing the socket?
It’s not dripping in grease here, but there is some residue.

The other half of the fryer doesn’t show overheating to this extent.

I’ll quote for installing 2 x 16A radials for the fryers, and do away with the 13A weak spot being the fuse… but no spare ways… gonna be a new board.
 
Back to a pub kitchen I worked in a month or so back. His fryers have overheated the sockets.

It’s a duel fryer… 2 x 3kW I recall, and I told him to plug them into different double sockets.
All good.

This is what met me this morning….

View attachment 99840View attachment 99841

13A fuse is welded into the plug, and has melted the front of the socket. Backside of socket has no signs of heat damage.

Replaced the socket and plug, but it’s likely to happen again.

13A plug should be fine for the fryer but it must be the duration that it’s on for during a weekend shift…
Or could it be down to hot oil splashing the socket?
It’s not dripping in grease here, but there is some residue.

The other half of the fryer doesn’t show overheating to this extent.

I’ll quote for installing 2 x 16A radials for the fryers, and do away with the 13A weak spot being the fuse… but no spare ways… gonna be a new board.

What brand is the socket, and how old is it?
 
In theory the fryers should be fine on a 13amp plug top as supplied by the manufacture

The fact the plug top is melting could be sign of a cheapo fake plug top ?
 
Back to a pub kitchen I worked in a month or so back. His fryers have overheated the sockets.

It’s a duel fryer… 2 x 3kW I recall, and I told him to plug them into different double sockets.
All good.

This is what met me this morning….

View attachment 99840View attachment 99841

13A fuse is welded into the plug, and has melted the front of the socket. Backside of socket has no signs of heat damage.

Replaced the socket and plug, but it’s likely to happen again.

13A plug should be fine for the fryer but it must be the duration that it’s on for during a weekend shift…
Or could it be down to hot oil splashing the socket?
It’s not dripping in grease here, but there is some residue.

The other half of the fryer doesn’t show overheating to this extent.

I’ll quote for installing 2 x 16A radials for the fryers, and do away with the 13A weak spot being the fuse… but no spare ways… gonna be a new board.

There will always be problems with a 3kw heating/ cooking load fed via a 13amp plug and socket. It's just the constant load causing heat.
Used to get a lot of it with 3 bar electric fires and these days 3kw fan heaters.
This MK one hidden behind a sofa....he thought there was a funny smell when he had his heater belting it out.

[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!
 
Posted before showing the internals of a twin socket melted due to overload, nothing tripped out as above, I wonder if an AFDD would have tripped and saved the damage to the socket? and more importantly stopped the room smelling of fish. 🐠

[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!
 
Last edited:

Reply to Dodgy trade pictures for your amusement! - 1 Million Views! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
560
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
760
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top