Does SPD MCB size matter? | Page 2 | on ElectriciansForums
Guest viewing is limited

Discuss Does SPD MCB size matter? in the UK Electrical Forum area at ElectriciansForums.net

oscar21

Nearly Esteemed
Joined
Nov 24, 2019
Messages
553
Reaction score
451
Location
North West
Does this matter? I've fitted a Fusebox consumer unit and I didn't have enough 32A MCB's but too many 6A's. The SPD is fed from a 32A one, what's the deal with swapping them around. They are voltage operated not current operated so should be fine right?
 
Yes, Like I say, if its private work we fit the Fusebox ones and if its council we fit also fit the Wylex ones with SPD's, Edwardes have a good deal on the wylex ones at the moment.

Off track slightly but the new Wylex stuff is pretty crap, you can't remove the din rail so have to take everything to bits just to get the RCD's out, they are exactly the same as the new Crabtree stuff as well so it all comes out of the same factory. And those metal blanks that slide about all ove the show when you are trying to get the lid on, woeful, although on the last board I did it came with different blanks that could clip in from the front.

Metal blanks can be a pain, but I understand they're used not only because it's a 'non combustible' material, but also because they require a tool to remove, whereas traditional blanks can be pulled out easily.

Wylex make blank modules that clip on the din rail and these also fit Crabtree starbreaker boards.
 
Does it really make that much difference if a 6A or 32A MCB is on the receiving end of a bolt of lightening?
Yes, but not for the obvious reasons.

As already mentioned most SPD are not rated to deal with a direct strike. The 'type 2' that most folks fit are intended for the 8us/20us waveform typical of induced lighting surges and similar when a strike hit something else and the power cables pick up the radiated EM disturbance.

They 'type 1' (or more commonly type 1+2) are rated for a portion of a direct strike, so if your building has a Lightning Protection System fitted then the assumption is a portion of the direct hit goes via the LPS to Earth, but some of it goes via the power cables and then the SPD has to divert it. This may have similar peak current ratings in the 10-50kA region but now the waveform is a 10us/350us shape (i.e. falr longer tail of decaying current) and as such it has about 17 times higher energy for a given current peak. That is why those SPD are often double-width and 5 times the price!

Back to the MCB, the problem here is inductance as at high frequencies (and the bulk of lightning power is around 100kHz, not 50Hz) that dominates circuit impedance over conduction resistance in most situation. That is why the regs have the 0.5m / 1m max cable length when fitting an SPD otherwise the series impedance of the cable loop increases how much voltage passes by to the supposedly protected installation.

When comparing a 6A MCB and a 32A MCB the "instant" magnetic trip point (instant in human terms, which is still several milliseconds, not microseconds) the trip point is just over 5 times higher, so your trip coil needs (for assumed same mechanical arrangement) 5 times the number of turns so the fault current applies the same force to initiate tripping. But inductance is proportional to turns squared, so your impedance to high frequencies is over 25 times higher!
 
A 6A would possibly trip well before the SPD had a chance to operate, rendering it useless. For the cost of another MCB…

As for RCBO vs dual rcd… it’s wrong to say he should fit an all RCBO board. There’s nothing in the regs preventing using a dual rcd….. and it might be all the customer can afford.
See Reg 531.3.2 unwanted tripping (ii) rcbos should be considered. Also see section 314
 
See Reg 531.3.2 unwanted tripping (ii) rcbos should be considered. Also see section 314
The way I read that is if you expect tripping then minimise it. Under a normal situation in a domestic setting you don't expect any RCD to trip whether its an RCBO or dual RCD board. However if you have a bank of computers that have a bit of earth leakeage then you might get unwanted tripping so use RCBO's instead.
 
The way I read that is if you expect tripping then minimise it. Under a normal situation in a domestic setting you don't expect any RCD to trip whether its an RCBO or dual RCD board. However if you have a bank of computers that have a bit of earth leakeage then you might get unwanted tripping so use RCBO's instead.
The reg states it just something to be considered. So its up to you if you choose to follow it. I prefer to use separate rcbos, but if the spec requires a split load board thats what will be installed . Just to add regarding spds. Hagers connect straight to the main switch with no OCD in the board
 
The reg states it just something to be considered. So its up to you if you choose to follow it. I prefer to use separate rcbos, but if the spec requires a split load board thats what will be installed . Just to add regarding spds. Hagers connect straight to the main switch with no OCD in the board
So do the Wylex and Crabtree ones, the first one I did I put the earth in the bottom and then thought why is there an earth position in the top as well. I'd set the board up with a space to the right of the main switch as well so it was all a kerfuffle to put it right again. I wish manufacturers would all stick to a similar design.
 

Reply to Does SPD MCB size matter? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
362
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
328
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
371

Similar threads

  • Question
It looked like the live connection side ( internally) burned against the neutral of the main switch
2
Replies
23
Views
1K
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2 3 4
Replies
47
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top