I know the answer, at least I think I do as I am now questioning myself! It's just I've seen a few jobs recently where the electrician (or who ever did the job) did not give any fault protection to the armoured cable, so I am wondering if I am missing something?

The most recent example from today is an EVCP which has been installed using SWA cable. The SWA goes directly into the consumer unit where it is supplied from a MCB. There is no relevant RCD protection on this cable. I realise it would not be required for TNCS or TNS as it would have fault protection from the main fuse. However, this is a TT, so there will be no fault protection on the SWA cable.

This is clearly wrong, isn't it?
 
32A B type Max Zs of 1.67 Ohm

would be tricky to achieve with TT earthing. :):)

although with a 100mA time delay rcd it would be easy to achieve ADS
 
Last edited by a moderator:
32A B type Max Zs of 1.67 Ohm

would be tricky to achieve with TT earthing. :):)

although with a 100mA time delay rcd it would be easy to achieve ADS
dont you mean 1.37 ohms or 1.1 ish at 80% values.
maybe with many rods mates or structural building earthing but i doubt it.
(RCD) Residual Current Device will comply but can lead to selectivity issues
 
I know the answer, at least I think I do as I am now questioning myself! It's just I've seen a few jobs recently where the electrician (or who ever did the job) did not give any fault protection to the armoured cable, so I am wondering if I am missing something?

The most recent example from today is an EVCP which has been installed using SWA cable. The SWA goes directly into the consumer unit where it is supplied from a MCB. There is no relevant RCD protection on this cable. I realise it would not be required for TNCS or TNS as it would have fault protection from the main fuse. However, this is a TT, so there will be no fault protection on the SWA cable.

This is clearly wrong, isn't it?
As others point out an RCD will almost certainly be required for fault protection as it is almost inconceivable that a reliably low Earth fault loop impedance will exist on a TT system (though technically permissible). That said the EVSE will nearly always require a maximum 30mA RCD for additional protection at this point. What EVSE has been installed, and is a circuit breaker actually OK for it?
 
As others point out an RCD will almost certainly be required for fault protection as it is almost inconceivable that a reliably low Earth fault loop impedance will exist on a TT system (though technically permissible). That said the EVSE will nearly always require a maximum 30mA RCD for additional protection at this point. What EVSE has been installed, and is a circuit breaker actually OK for it?
ohme pro.
It has type A RCD and pen fault protection inside it, but It's the cable leading up to it that I'm concerned with.
The customer got me to quote, then went with someone else, who I'm guessing wasn't an electrician as there are also other things wrong. I was doing a hob install for them, so had a quick look at the EVCP install.

Top entry into a weatherproof box,
No fault protection on cable.
SWA not glanded properly into the CU.
Armour not earthed
I'm guessing... no EIC or notification.

It's just horrible.
 
ohme pro.
It has type A RCD and pen fault protection inside it, but It's the cable leading up to it that I'm concerned with.
The customer got me to quote, then went with someone else, who I'm guessing wasn't an electrician as there are also other things wrong. I was doing a hob install for them, so had a quick look at the EVCP install.

Top entry into a weatherproof box,
No fault protection on cable.
SWA not glanded properly into the CU.
Armour not earthed
I'm guessing... no EIC or notification.

It's just horrible.
I can't see how the RCD in the Ohme Pro could be to either BS EN 61008 or BS EN 61009.
 

Reply to Does SWA need RCD on a TT? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
742

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top