Does this require Main Bonding? | Page 2 | on ElectriciansForums
Discuss Does this require Main Bonding? in the UK Electrical Forum area at ElectriciansForums.net
HappyHippyDad
Supporter
Gloucestershire
The water pipes enter the house in metal, then there are a few cm's of copper after the stop cock and then plastic. It is hidden behind the kitchen draws (which can be removed to access).
Does this require Main Bonding? The stop cock tests as 0.36Ω to earth, it is TNCS.
I just cant see how fitting a Main Bonding cable achieves anything in this case?
Your own test has determined that the incoming pipe is extraneous so needs bonding as per BS7671:2018.
Whether or not it does anything or not is a mute point as BS7671 does not give much wriggle room. Is it extraneous? Yes. Is
there an insulating
section at the incoming point to the property? No. So it requires bonding whether we like it or not. There is nothing in BS7671 that states the main incoming water pipe needs to be accessible - 544.1.2.
The OP appears to state there is an insulating section close to the point of entry. Of course the stopcock will be extraneous, but the regulations clearly state now that a short section of incoming pipe which has an insulating section close to the point of entry will not require main bonding.
The insulating section has to be at the point of entry.
Only applies if a blue plastic service pipe, does not apply if a metal service pipe!
Reply to Does this require Main Bonding? in the UK Electrical Forum area at ElectriciansForums.net
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right