I quite like them as it gives you the chance to exercise your interpretation of the regs and get other opinions, regardless of whether they change your views or not.
It's one of the things I miss from my old job, the ability to quickly bounce ideas around and discuss them. Working solo isn't conducive to it... well, it's not if you don't want to end up in a straight jacket
So if they were indeed two circuits by design but we can change that by connecting them together at the CU, can we then lump three or four or even more to one breaker, loads considered?
I would say theoretically yes on the proviso that they are being moved to a breaker of the same rating as their original design or less. But loading aside there are other factors to consider like the ability to safely terminate the cables at the DB. There will be a point where it's just not physically possible to do it safely without say using a much larger cable and terminating the individual cables in a junction box.
Also if you had a long run of say 6.0mm SWA on a 20a OCPD and it was drawing 11a, and you had another circuit on a 20a which was 2.5mm T&E and drawing 7a could these be lumped together as one circuit even though they are of different sizes and even types? What would go on the certificate in respect of cable size?
In their own right, both cables would be adequately protected by a 20A OCPD, and the total combined load (assuming that is the maximum you've stated) would not result in nuisance tripping due to unintentional overload.
So yes, theoretically they could be combined. I'd record the difference in cable size by stating MIXED in the size columns and then expressing that on a continuation page. Same as I would for any circuit with mixed conductor sizes. The lollipop being a fine example - not that I've ever done this.
And of course providing due regard was given to the other parts of the regulations regarding division of the installation (i.e. minimise risks, inconvenience etc.).
However, would I do either of these things? I'm not sure. I might at a pinch (as an example, the situation where you need another breaker and cost is a major factor) but ordinarily I doubt I would.
Well quite, I think it's another case of what the regs allow vs. what's widely accepted as good practice. Do I like seeing four conductors in an MCB... not really, is it strictly against the regs... probably not providing the other provisions of the regulations are catered for (such as overload protection, division of circuits etc.).
In this case, I can see the logic behind the OPs reason for doing it, would I have done the same? Probably not. Do I think it's acceptable? Well clearly yes I do, I just don't think it's good practice and I would probably have just left it as it was.
I thought you'd pick that one! So at the origin of the installation, is the 'point of supply' the incoming cables connect to the head, the main OCPD, if so which side of it, or the point at which the tail connects to the OCPD? It doesn't say so again you cannot go definitive on that.
I'm just not trying to overthink it too much. A cable doesn't supply electricity, it carries it, so in this case I consider the source of power to be the protective device as the origin.
Why? I fundamentally disagree with this. I believe that it is absolutely the cabling that defines the circuit. Are you saying that a breaker with no cable connected is still a circuit? We are getting down the semantics of what the definition is and I think this is where you and I differ.
No, I would consider a breaker with no cable connected as a spare way.
The regs state specifically that this is allowed from a ring final circuit and so this is also a red herring.
Do they though? The only section that gives any definitive guidance about the topology of a ring circuit is 433.1.204, and it only specifies the topology in terms of acceptable cable loading.
The only place I've been able to find a statement to the effect it's allowed is in the OSG and it doesn't reference a regulation to back it up.
So why wouldn't you do it then?
Because I don't consider it to be good practice, plain and simple. Regardless of whether I consider it to be allowed by the regulations, it doesn't feel like it's something we should be indulging in at every opportunity
Finally, if you are correct and I am not, then what is the meaning of 314.4?
It basically requires that each final circuit is capable of being isolated completely from a single point. I can't say much more than that without saying pretty much what it says.