The Reg is 314.4.
You can run a spur from the OCPD from a ring and comply as it is specifically allowed in BS7671.
You cannot comply with BS7671 by bunching circuits such as lighting or radials in the same OCPD. It is non compliant.
And just to throw a rather large spanner in the works, the regulations also state that you are allowed deviations from the regs if you can prove that they are electrically as safe as the regs require them to be. This is what the deviations box is for in the EIC. The regs are of course non statutory so there is scope to adapt. It would still be a non compliance but under the regs it is allowed as long as you list it as a non compliance and justify your reasoning for doing it.
You can run a spur from the OCPD from a ring and comply as it is specifically allowed in BS7671.
You cannot comply with BS7671 by bunching circuits such as lighting or radials in the same OCPD. It is non compliant.
And just to throw a rather large spanner in the works, the regulations also state that you are allowed deviations from the regs if you can prove that they are electrically as safe as the regs require them to be. This is what the deviations box is for in the EIC. The regs are of course non statutory so there is scope to adapt. It would still be a non compliance but under the regs it is allowed as long as you list it as a non compliance and justify your reasoning for doing it.