Easyfox Would the 16mm MEC need protecting? CheersSwitch fuse at the meter end then
Use 25mm 2 core swa & a seperate 16mm mec.
.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Doing my first sub-main in SWA. in the Talk Electrician area at ElectriciansForums.net
Easyfox Would the 16mm MEC need protecting? CheersSwitch fuse at the meter end then
Use 25mm 2 core swa & a seperate 16mm mec.
.
I only use the armour as a way of beefing up the earth and mech protection.
If your not running three core 16mm yoy should run a seperate 16mm MET
Sorry to bang on about it but where does it say about running a separate earth and why isn't the armouring sufficient.
There is no requirement if you are using 3 core SWA, but obviously you need one if using 2 core plus seperate earth.
However, if there is no need for mechanical protection and it is going to be run in trunking, then i would suggest you ask your supplier for 16mm split concentric cable.
Doddle to run and terminate with standard plastic compression glands.
Have a look here:
Electrical Cable - Split Concentric Cable BS7870
wow! never seen that before! whats with all the neutrals???
last time i used some of this stuff we had to heat shrink the neutrals and earth