D'you think it would be ok to run split con through a communal entrance hall (all indoors) into the flats without trunking, just clipped to the surface? If not, would plastic trunking be OK?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Doing my first sub-main in SWA. in the Talk Electrician area at ElectriciansForums.net
Sorry to be the bearer of doom but if you used Split-Con you would have to RCD protect the cable, bury it greater than 50mm or protect it with earthed capping/conduit, as it does not have a earthed protector and the Neutral is classed as a Line conductor.
Trying to get all the neutrals into the termination would be a pain as well.
As for not sleeving them, would you not sleeve CPC and Neutral conductors in a CU?