D'you think it would be ok to run split con through a communal entrance hall (all indoors) into the flats without trunking, just clipped to the surface? If not, would plastic trunking be OK?
Sorry to be the bearer of doom but if you used Split-Con you would have to RCD protect the cable, bury it greater than 50mm or protect it with earthed capping/conduit, as it does not have a earthed protector and the Neutral is classed as a Line conductor.
Trying to get all the neutrals into the termination would be a pain as well.
As for not sleeving them, would you not sleeve CPC and Neutral conductors in a CU?
There is no requirement to rcd protect a split con cable that is surface mounted, providing it is out of reach and cannot be damaged. No different from t&e.
Obviously if it is buried then yes, but to be honest, i would do everything i can to avoid an RCD on the front end of it, even if it meant trunking. Its a piece of cake to work with and looks a lot neater.
There is no problem getting the neutrals into a termination point. Just a little care and time taken to do the job.
Why would you need to sleeve a neutral conductor in a cu?
CPC's yes.
Reply to Doing my first sub-main in SWA. in the Talk Electrician area at ElectriciansForums.net
totally agree
Sounds more positive.