And just to confirm i ran down and checked, i could turn the blades by hand when unplugged so no brake present.
That doesnt proove a motor doesnt have a brake squire...motors can be stopped by dc injection...
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss DOL starter 7.5HP, 3 ph motor in the Commercial Electrical Advice area at ElectriciansForums.net
And just to confirm i ran down and checked, i could turn the blades by hand when unplugged so no brake present.
The motor is a David Brown....
That doesnt proove a motor doesnt have a brake squire...motors can be stopped by dc injection...
Lol.
A1/A2 will be your coil and is energised by the control circuit as my previous post............voltage needs to be checked as it could be a 230v or a 415v coil and that would be your control circuit voltage so you don't really want to be taking that to your lid switch
We use safety PLC here now. There are lots of safety relays and I suppose it depends on what category of stop you require as to which type of relay you use.
This all depends on the risk assessment that should be done on the mixer (if you are upgrading the mixer to current regs).
But if what Tony says is true for your mixer and that the motor will stop straight away when the lid is lifted then there may be no need for a safety relay.. All depends on the risk assessment mate.
Paddle mixers depending on the product plasticity will normally stop dead IF LOADED.
Unloaded they will run on.
This is where common sense has to play its card.
Most of my work has involved centrifugal fans up to 2500HP. Are you going to try to stop that quick?
No amount of safety relays can take out kinetic energy. 20 minutes for a 2000HP fan to stop due to the fan impellor acting as a flywheel.
Reply to DOL starter 7.5HP, 3 ph motor in the Commercial Electrical Advice area at ElectriciansForums.net