Hi all,

As the title suggests, I'm looking for a little bit of guidance.

Long story short... kitchen remodel, was asked to install a heavy duty supply for an induction hob on short timescales as ceiling was going to be closed.

Only sizeable cable I had to hand was 10mm.

Now, in a happy turn of events, it turns out that the induction hob isn't that hungry and only needs to plug in, but the oven and microwave also require supplies. None of them are over 16A.

So my original plan was to install a BG shower CU, switch out the breakers for 16A (one for each appliance) and supply this using the 10mm on a 50A breaker from the main DB. The new CU was to be mounted on the wall, making an obvious accessory safety zone.

However, due to the construction of the kitchen units, I felt it better to have the CU inside a cupboard rather than cut a portion of the backboard away.

Where I'm seeking guidance is that this now means the 10mm is concealed in the wall, from ceiling to just below the top of the cupboard. Along the rest of it's run, it is installed in a manner (i.e. it's not at risk of damage and it's not concealed in a wall) that means it's fine to be connected to the non-RCD side of the board (the new CU has RCD protection in it).

So I have a length of cable about 10-12" buried in the wall. Due to it's location I don't believe it is at risk of being damaged by screws as it is unlikely anyone will want to hang anything there because it's effectively behind the cupboard.

I have placed a warning sticker on the top of the cupboard (Danger Concealed Cable - This includes an arrow aligned with the vertical drop of the cable). I'm going to record full details on the certificate of the location of the cable and my reasoning as to why this is acceptable.

Acceptable or not? Is this kind of departure allowed in domestic and if so is it sufficient to include your reasoning in the certificate or is there a template risk assessment I would need to use?

Your comments and thoughts are most welcome :)
 
My opinion with such occasions is that common sense has to apply, and I would say there is nothing wrong ..... But why not put the circuit on a rcbo?

Old Memera board and no spare ways from what I can see, so the old 32A cooker circuit is being decomissioned and replaced with a 50A feed to the sub-board.

Edit:-

Just to be clear, the current board has one RCD and the cooker circuit isn't on it.
 
It's maximum rated power is 3kW, and it comes fitted with a 13A plug. It's not being connected to the ring final that supplies the kitchen.

It's on it's own 16A radial circuit (2.5/1.5mm T+E - New sub-board -> 20A DP Switch -> 13A socket outlet behind units/in kickspace).
 
I have placed a warning sticker on the top of the cupboard (Danger Concealed Cable - This includes an arrow aligned with the vertical drop of the cable). I'm going to record full details on the certificate of the location of the cable and my reasoning as to why this is acceptable.
now how is going to ask for a test certs when drilling
a wall there then.
 
Does the cable run have to be plastered over or can it be left exposed or have suitable mechanical protection such as a metal plate?
 
With Departures, you as the designer have to attest that the departure offers the same degree of safety as would be provided by compliance with the Regulations.

I think that's what my concern is. As it is I can't say it's as safe because it's not, which leads on to Strima's post which I was going to reply to you with.

Does the cable run have to be plastered over or can it be left exposed or have suitable mechanical protection such as a metal plate?

Time to break out the metal capping and pop a couple of layers of that over it (fingers crossed the customer hasn't filled the channel yet)!

now how is going to ask for a test certs when drilling
a wall there then.

They don't need to see a test certificate... there is a warning notice on the top of the cupboard that clearly states there is a concealed cable and identifies it's location.
 
Does the cable run have to be plastered over or can it be left exposed or have suitable mechanical protection such as a metal plate?

To answer your specific question Strima... no it cannot be exposed. Client's wife is a bit OCD about cables and holes in walls.

Part of the reason the unit was moved into the cupboard was because it was there with three lengths of T+E hanging out of it ready for the terminations and it freaked her out a little, so all the cabling has to be hidden once the kitchen is finished.

Lovely couple, just a little crazy :)
 
I'd look at more substantial methods of protection to satisfy the requirements of the regs.

Any suggestions? Short of hacksawing some 25mm conduit in half lengthwise, I'm a little short of ideas. I have out of interest learnt how easy it is to drill through the capping without really trying, so yes, I know where you're coming from.
 
what about putting a big f**k off big arrow on the wall for that then ,unless to have a head like a giraffe.

The cable runs about 10-12" in the wall... from the ceiling to just under the top of the cupboard... if you're up there to drill a hole, I think a yellow warning sticker will stand out (at least until it's covered with 10+ years a grime).
 
Any suggestions? Short of hacksawing some 25mm conduit in half lengthwise, I'm a little short of ideas. I have out of interest learnt how easy it is to drill through the capping without really trying, so yes, I know where you're coming from.

Either fully enclosed in earthed conduit or I know there are companies that sell substantial
shields/capping for buried cable, mostly employed for buried tails where RCD protection is not desirable.
 
To answer your specific question Strima... no it cannot be exposed. Client's wife is a bit OCD about cables and holes in walls.

Part of the reason the unit was moved into the cupboard was because it was there with three lengths of T+E hanging out of it ready for the terminations and it freaked her out a little, so all the cabling has to be hidden once the kitchen is finished.

Lovely couple, just a little crazy :)
What about some anti-vandal guard, you'd have trouble sticking a nail through that... :D

RONBAR FACTORS LTD UK Manufacturing supply for electrical wholesalers - Anti Vandal Guard - http://s413652122.initial-website.co.uk/products-1/anti-vandal-guard/
 
A short section of 3mm thick steel C section over the cable and plastered over would obviate the need for an RCD, since it is a variation you can clearly charge the extra for this protection.
It would however be up to the installer to assess the level of safety as meeting the requirements for a departure if you were not to do this.
 
It's either metal-detection gear,at each door to the kitchen,to prevent drilling equipment being brought in...

...or upstream protection. If you are concerned about this situation,i would aim for the latter :)
 
I think I'm going to cut a length of 25mm conduit and slice it open with my grinder, cutting a slot big enough to slip over the cable. Drill a small hole and earth it with a crimp and self tapper to some 2.5mm earthing cable. Being sure to file off the end of the screw.

Thanks for the advice guys, much appreciated.
 

Reply to Domestic Departure from BS7671 - Advice in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
378
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
4K
  • Question
These folks sell covers (vented and non-vented) and related retaining clips...
Replies
14
Views
5K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
  • Question
Youre in the same boat as me. I was previously with niceic and later on, napit. No issues. I didn't bother finishing my nvq3 as in 2010 during the...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks