Hi all,

As the title suggests, I'm looking for a little bit of guidance.

Long story short... kitchen remodel, was asked to install a heavy duty supply for an induction hob on short timescales as ceiling was going to be closed.

Only sizeable cable I had to hand was 10mm.

Now, in a happy turn of events, it turns out that the induction hob isn't that hungry and only needs to plug in, but the oven and microwave also require supplies. None of them are over 16A.

So my original plan was to install a BG shower CU, switch out the breakers for 16A (one for each appliance) and supply this using the 10mm on a 50A breaker from the main DB. The new CU was to be mounted on the wall, making an obvious accessory safety zone.

However, due to the construction of the kitchen units, I felt it better to have the CU inside a cupboard rather than cut a portion of the backboard away.

Where I'm seeking guidance is that this now means the 10mm is concealed in the wall, from ceiling to just below the top of the cupboard. Along the rest of it's run, it is installed in a manner (i.e. it's not at risk of damage and it's not concealed in a wall) that means it's fine to be connected to the non-RCD side of the board (the new CU has RCD protection in it).

So I have a length of cable about 10-12" buried in the wall. Due to it's location I don't believe it is at risk of being damaged by screws as it is unlikely anyone will want to hang anything there because it's effectively behind the cupboard.

I have placed a warning sticker on the top of the cupboard (Danger Concealed Cable - This includes an arrow aligned with the vertical drop of the cable). I'm going to record full details on the certificate of the location of the cable and my reasoning as to why this is acceptable.

Acceptable or not? Is this kind of departure allowed in domestic and if so is it sufficient to include your reasoning in the certificate or is there a template risk assessment I would need to use?

Your comments and thoughts are most welcome :)
 
I'd look at more substantial methods of protection to satisfy the requirements of the regs.

Any suggestions? Short of hacksawing some 25mm conduit in half lengthwise, I'm a little short of ideas. I have out of interest learnt how easy it is to drill through the capping without really trying, so yes, I know where you're coming from.
 
what about putting a big f**k off big arrow on the wall for that then ,unless to have a head like a giraffe.

The cable runs about 10-12" in the wall... from the ceiling to just under the top of the cupboard... if you're up there to drill a hole, I think a yellow warning sticker will stand out (at least until it's covered with 10+ years a grime).
 
Any suggestions? Short of hacksawing some 25mm conduit in half lengthwise, I'm a little short of ideas. I have out of interest learnt how easy it is to drill through the capping without really trying, so yes, I know where you're coming from.

Either fully enclosed in earthed conduit or I know there are companies that sell substantial
shields/capping for buried cable, mostly employed for buried tails where RCD protection is not desirable.
 
To answer your specific question Strima... no it cannot be exposed. Client's wife is a bit OCD about cables and holes in walls.

Part of the reason the unit was moved into the cupboard was because it was there with three lengths of T+E hanging out of it ready for the terminations and it freaked her out a little, so all the cabling has to be hidden once the kitchen is finished.

Lovely couple, just a little crazy :)
What about some anti-vandal guard, you'd have trouble sticking a nail through that... :D

RONBAR FACTORS LTD UK Manufacturing supply for electrical wholesalers - Anti Vandal Guard - http://s413652122.initial-website.co.uk/products-1/anti-vandal-guard/
 
A short section of 3mm thick steel C section over the cable and plastered over would obviate the need for an RCD, since it is a variation you can clearly charge the extra for this protection.
It would however be up to the installer to assess the level of safety as meeting the requirements for a departure if you were not to do this.
 
It's either metal-detection gear,at each door to the kitchen,to prevent drilling equipment being brought in...

...or upstream protection. If you are concerned about this situation,i would aim for the latter :)
 
I think I'm going to cut a length of 25mm conduit and slice it open with my grinder, cutting a slot big enough to slip over the cable. Drill a small hole and earth it with a crimp and self tapper to some 2.5mm earthing cable. Being sure to file off the end of the screw.

Thanks for the advice guys, much appreciated.
 
I think I'm going to cut a length of 25mm conduit and slice it open with my grinder, cutting a slot big enough to slip over the cable. Drill a small hole and earth it with a crimp and self tapper to some 2.5mm earthing cable. Being sure to file off the end of the screw.

Thanks for the advice guys, much appreciated.
Remember a 2.5mm² protective conductor not part of a cable would need to be protected against mechanical damage, 4mm² otherwise.
 
A bit out there and not considered in the regs!! but have you considered kevlar or composite sheets? they come in thicknesses of a couple mm, you can take back the top layer of plaster around the cable then apply the small sheet over the chase... using expoxy resin/adhesive affix to wall over cable and either side. a bit of epoxy over top its like steel and bullet proof! a drill wont go through that easily... then apply pva to the top, its then good for a skim of plaster to bring flush with rest of wall, Its what is used in forces to repair holes from things that go bang! so clearly strong enough, the sheets are a bit of a bugger to cut to size though but a small one is about a tenner online and epoxy is everywhere in shops.
I used it once upon a time to protect a wiring loom on some equipment, wrapped it up in the kevlar sheet, applied the 2 part epoxy and was good for use. idea being to protect it from potential damage in event of a explosion or blast damage.
 
Last edited:

Reply to Domestic Departure from BS7671 - Advice in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
240
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
634
Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
578

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top