View the thread, titled "Domestic PIR No RCD - can I / can't I?" which is posted in Domestic Electrician Forum on Electricians Forums.
M
mattcos1972
Evening all!
Quick domestic PIR question.
I have been asked to PIR on a home for a friend of mine. The installation is perfectly sound throughout the home. Lighting is split into 2 circuits, there are a total of 5 ring finals for the sockets as extensions / loft conversions have been added over the years. All spurs are fused, including boiler etc.
All dead tests, Ze, PFC & Zs are well within their parameters. IR is off the scale and every ring test is spot on. Smoke alarms are interlinked, mains powered and battery backed up, even the doorbell is fused off a lighting ring. Basically it's spot on....only problem is there are no RCDs.....Can I pass it on a PIR? The installation went in in 2002. I've not been sparksing for that long so I don't know what the regs were at the time?
Thanks in advance for any help, opinions, advice etc........
Oh and yes, I am 2391 before you ask!! :p:p:p:p
The above is the op. Nowhere does he say anything about bad bonding, he's asking about the lack of rcd in an installation from 2002 (16th regs).
Bpg page 15 right hand side, third comment about rcd. I'll go with that one and give it a code 4 and suggest to customer to install rcds if they want. It's not a requirement for the date of that installation.
I may agree or not
my opinion
If it complies to the 16th then it's OK, providing:
There is supplimentary bonding in the bathroom with a coninuity od < 0.05 ohms across it all
and
there is an RCD on the sockets (or a RCD socket marked 'for equipment outdoors'
If there is NO RCD and NO supplimentary bonding then i would fail
It has to comply with the old regs- not just the bits you pick and choose
Since the 15th Edition (from 1984 to my knowledge) RCD protection was a requirement for any socket outlet with potential use for out door equipment.
So there's a good possibility it never met the 16th and having RCD protection for the use of outdoor equipment of paramount imo. So I would code 2.
So you would make every house with no rcd unsatisfactory
When you do a pir you are testing if it is safe dose it dosconnect in time and do they have a rcd socket for out sIde.
Or will they sign to say they don't use electrical things outside
I think like every PIR as you are the tester you will need to decide what is safe and what is not. If I Found a ground floor socket outlet circuit that did not have RCD protection and there was a likelyhood that mobile equipment for outside use was being plugged into this then I would code it a 2 as per the ESC guidlines.
If I saw though on this circuit an RCD socket outlet near the back door or the window I would expect any outside equipment to be plugged into this and code it a 4, it really is down to the inspector to make these calls.The ESC guidance notes the OSG are all great guides, but in the end just guides, the final call is the testers.
There is one simple answer to this code 4 it and put a reccomendation for RCD protection it was wired in 2002 so it should have had RCD's bonding etc installed as it would have been to 16th edition , i do agree with duram though , but heres one for thought Tony cable from the NIC stated install a main switch RCD if they dont want to pay for a CDU upgrade , in my eyes its not suprising we get confused
I totally agree with Tony Cable, the risk of non-rcd protected sockets supplying portable equipment outdoors far outweighs the ridiculous 'old woman falling down the stairs in nuisance tripping incident' rubbish!
Perfect answer
Remember when we PIR we are interpreting the current regs against actual installation I am looking at
Although it's a matter of opinion on how you pass / fail a PIR, there seems to be a difference on opinion as and when things fail
You can't look at the regs and pick and choose the bits you want.
As far as the 17th Edition goes, I think RCD'ing lights is a step too far. The days of plugging and iron into a lighting point are long gone
These days people like to sue electricains (not had any yet!), but the regs, the OSG and the ESC guides are there for guidance- if you use the guide and somoene tries to pull you up they are on to plums
It's a bit like king canute and the tide- you need to go with the flow- not agree with it wholehartedly, but go with it
I agree with you mate and im sure it was me with the old woman incident which came from a NIC guy called bill when he told us we couldnt install a main switch RCD , then on the next breath he told us if we find a bad installation install a main switch RCD lol
Don't forget, you aren't 'RCDing lights' per se, you're protecting cables buried in walls at depths of less than 50mm etc etc whether that's a lighting circuit or an immersion is not the actual reason.
Reply to the thread, titled "Domestic PIR No RCD - can I / can't I?" which is posted in Domestic Electrician Forum on Electricians Forums.